    HOT Temp buss bar 100A House Service panel
    In replacing a 15A circuit breaker found that one of the buss bars is getting very hot.
    Before connecting, installing breaker only, buss bar is hot enough to heat up the breaker?
    Probable causes? There are more breakers on one buss side, unbalanced load.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    May 27, 2009, 08:31 PM
    Loose breakers, possibly an overloaded buss. If your comfortable with a clamp on ammeter, check the draw on the panel. Balancing out the panel may be something you can try, but do the troubleshooting. How old is the panel?
    jerro's Avatar
    jerro Posts: 172, Reputation: 5
    Junior Member
     
    #3

    May 27, 2009, 08:39 PM

    What was the reason for changing the breaker? If the breaker got hot instead that could cause the buss bar to get hot and would take a little time to cool down before installing a new breaker. Check to see if any other breakers are hot.
    chasleroy's Avatar
    chasleroy Posts: 7, Reputation: 1
    New Member
     
    #4

    May 27, 2009, 09:02 PM
    I will investigate further... including clamp-on for amp readings. Note: The buss bar was hot before installing breaker. Thanks,
    chasleroy's Avatar
    chasleroy Posts: 7, Reputation: 1
    New Member
     
    #5

    May 29, 2009, 02:38 PM
    I measured amps on high side of 100A breaker: Two load readings Red: 35/28 and 55/40 amps. Don't think this is enough unbalance to cause heating up buss bar? Can someone conrirm? Also, is probable that any one of the breakers was defective, it would act as bad connection and cause the bar to heat up? Thanks
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #6

    May 29, 2009, 03:16 PM
    No, that's not excessive. And you may be correct about the breaker. Did the buss cool after you switched out the breaker?
    chasleroy's Avatar
    chasleroy Posts: 7, Reputation: 1
    New Member
     
    #7

    May 29, 2009, 09:39 PM
    We are back to normal temp and load conditions. Plan is to check panel and all the breakers and connections to see if we can identity the cause. Thanks for assist.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Updating service panel to 200 amp with feeder to 100 amp panel in old house [ 8 Answers ]

I currently in the process of converting 1000 sq ft of attached garage into living space while doing this we are updating electrical service to 200 amp new service, there is 100 amp service in the old part of the house which will remain but need to be sub paneled from the new 200 amp service. I...

Can I go smaller than 100A sub-panel? [ 1 Answers ]

I want to wire a detached garage/workshop, and I was wondering... Is 100A as small as I can go? If not... what are the smaller size sub-panels that they make... that are legal as far as code allows... Thanks in advance for the help.

Wire to a 100A sub-panel [ 1 Answers ]

I want to run copper wire from my 200Amp main electrical panel to a 100Amp sub-panel. The 100Amp panel will feed a heat pump compressor, air handler with heat strips (total load = 70 amps) and about 4 20 amp outlet lines. I have previously wired a 60 Amp sub-panel in this house. The panels would...

100A Service [ 1 Answers ]

How do I Install a 100 amp single phase three wire service?


View more questions Search