    562349's Avatar
    562349 Posts: 2, Reputation: 1
    New Member
     
    #1

    Jun 21, 2013, 11:54 AM
    Main 200 amp. Installing a 200 amp sub-panel. Wire size jumper to connect(2 /100 amp)
    Installing a 200 amp.sub-pane (type D- Hom), the main panel is 200 amp.also, I'm using 2 /100 amp. Breakers. My question is : what wire size do I need for the jumper to connect the two breakers.
    I'm using #2 X3 and #4 ground wire to connect the sub-panel, do I need the same#2 for the jumper?
    Or what will be the best way to connect it, Six lines plus ground to the sub-panel or Jumper, and again what wire size?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jun 21, 2013, 01:23 PM
    First off, a double pole 100A breaker is not 200A. It is a 100A breaker.

    You have a main panel, fed from the meter. Then you have a sub-panel, with a feeder from the main to the sub.
    What are you referring to as a jumper? I can't grasp what you are describing.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire size required from 200 amp main to 100 amp sub panel [ 1 Answers ]

The sub panel is located @75 feet from main panel.

Can I downgrade a 200 amp service with a 200 amp main by adding a 100 amp breaker to [ 1 Answers ]

Can I downgrade a 200 amp service to a 100 amp service by adding a 100 amp breaker to the panel

Can you connect a 100 amp double throw safety switch to a 200 amp main [ 3 Answers ]

Can you connect a 100 amp double throw swicth to a 200 amp main disconnect

100 amp main, 100 amp service wire, 200 amp sub panel? [ 2 Answers ]

I am moving my sub panel and upgrading to a 200 amp service, but in phases. The first phase is to move the panel due to some remodeling. I want to put a 200 amp panel in the laundry room with a 200 amp breaker. I have 100 amp feeder wire going to it (AL 2/2/2). Outside I have the meter can and...

Wire size for a 100 amp sub panel 200 feet away [ 8 Answers ]

I have a 200 amp main panel in my house and I just built a garage and am planning on putting a 100 amp sub panel in the garage. The garage is about 200 feet from my house and it has a 2 inch pvc stubbed out underground. I am wondering what size aluminum I would need to feed it, and if I can use a...


View more questions Search