    emmynet's Avatar
    emmynet Posts: 6, Reputation: 1
    New Member
     
    #1

    Sep 26, 2013, 11:56 AM
    How Do I Increase Frequency In 2.2KV Generator?
    I have a 2.2KVA (2.5KVA at Max) Electric Generator, within about 200 Hours of usage, I observed that the frequency droped to 25 (as indicated on the Hour Meter to read: F-25) from 60.

    The Voltage remain costant as 230V, so please how do I increase the Frequency back to 60 as the Generator can no longer carry Fridge as when the Freqency was 60.
    sinnadurai's Avatar
    sinnadurai Posts: 127, Reputation: 2
    Junior Member
     
    #2

    Sep 26, 2013, 10:30 PM
    Did you check the speed of the engine and AVR settings?
    emmynet's Avatar
    emmynet Posts: 6, Reputation: 1
    New Member
     
    #3

    Oct 1, 2013, 02:07 PM
    Thanks for responding to my question.

    Really I do not know to check or confirm the Speed, except through the audible noise from the generator that will denote that, it is running really fast. The LCD on the on the generator only display:

    *Voltage
    *Frequency
    *Hours/Minutes of Usage
    *Cumulative Hour of usage.


    When I powered up the generator few hours ago, the generator was running low in speed (noticed via the sound), but the Voltage still remain 230V, I then noticed that the Frequency was 60Hz, but after running for a few minutes, the generator increased automatically in speed the frequency dropped to 26Hz!

    After noticing the above, I then manually reduced the Running Speed of the Generator, to my surprise, the frequency promptly increased to 60Hz/65hz!

    With the increase in the frequency, I observed that, the Fans in the House increased blowing/rotating speed too!

    Kindly advice please, can I continue to use the generator in the manner? I mean, I hope it will not have negative effect on the generator or any house appliance.

    Thanking you once again for your help.
    sinnadurai's Avatar
    sinnadurai Posts: 127, Reputation: 2
    Junior Member
     
    #4

    Oct 1, 2013, 11:17 PM
    Use a tachometer(mechanical or electronic)
    smoothy's Avatar
    smoothy Posts: 25,490, Reputation: 2853
    Uber Member
     
    #5

    Oct 2, 2013, 05:09 AM
    This is a small portable Generator... I'm betting he's losnig one set of the poles on the generator head at times. Since most of these are 4 pole generator heads... losing 1/2 would drop your frequency in 1/2 and the reduced load might play a little havoc with the mechanical governor. (though it really shouldn't by much)
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #6

    Oct 2, 2013, 09:13 AM
    Have all the basic checks been done? Does this model have brushes?
    Are all connections tight, inside and out?
    emmynet's Avatar
    emmynet Posts: 6, Reputation: 1
    New Member
     
    #7

    Oct 3, 2013, 02:41 AM
    Quote Originally Posted by hfcarson View Post
    have all the basic checks been done? Does this model have brushes?
    are all connections tight, inside and out?
    Thanks for your respond.

    Yes, the Model uses Brushes.

    Regard,

    Emmy.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #8

    Oct 3, 2013, 04:25 AM
    Replacing the brushes may solve the problem...
    sinnadurai's Avatar
    sinnadurai Posts: 127, Reputation: 2
    Junior Member
     
    #9

    Oct 3, 2013, 06:06 AM
    Non-contact type tachometers are available
    emmynet's Avatar
    emmynet Posts: 6, Reputation: 1
    New Member
     
    #10

    Oct 3, 2013, 01:08 PM
    Quote Originally Posted by sinnadurai View Post
    non-contact type tachometers are available
    Thanks for the respond.

    At the moment, am running the Generator with Frequency at 60Hz, that is, after I have reduced the engine speed by adjusting the Speed Control (on the Governor Control and also at the top of the Carburetor)!

    With the Frequency at 60Hz, my refrigerator and Fans are now working fine. However, my fear is that, is that the best solution to this problem?
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #11

    Oct 4, 2013, 04:33 AM
    Best solution? That is yours to decide...
    If you verified that the brushes are good and do not need to be replaced, that all connections are tight, all wiring is in good condition, then the generator may need to be replaced...
    The next move is yours...
    emmynet's Avatar
    emmynet Posts: 6, Reputation: 1
    New Member
     
    #12

    Oct 4, 2013, 10:17 PM
    Quote Originally Posted by hfcarson View Post
    best solution? That is yours to decide...
    If you verified that the brushes are good and do not need to be replaced, that all connections are tight, all wiring is in good condition, then the generator may need to be replaced...
    the next move is yours...
    Thanks for the respone once again.

    With the reduction in the engine speed that have given me the desire frequency rate of 60hz, has that not solve the problem? Or will it resolve to creating another problem in the near future?

    Thankx.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #13

    Oct 7, 2013, 04:11 AM
    Well let's see... so far you have done nothing...
    So far all I have recommended is that you check the brushes...
    Checking the brushes will cost about two minutes... if they are very short then sometime
    Soon you will damage the generator.
    If the brushes are good then the problem is elsewhere and we have narrowed the search and can then test or examine other possibilities...
    What would you like to do?
    emmynet's Avatar
    emmynet Posts: 6, Reputation: 1
    New Member
     
    #14

    Oct 11, 2013, 03:00 PM
    Thank you so much for your respond.

    Yes, I have checked the brushes and find out that, the brushes are still long and good.

    So, what next can I do please?

    Thanks,

    Emmy.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Why does my generator frequency fluctuate under load? [ 5 Answers ]

Generator frequency

Use inverter to increase power output of a generator [ 7 Answers ]

Hello does anyone know if it is practical or even possible to amplify the power of a small generator using a large watt inverter? Say you have a 2 or 3 HP 1000 watt generator and you hook it up to a 5000 watt inverter. What kind of power will you be NOW able to generate? Doesn't the horse power of...

Generator over frequency fluctuation [ 1 Answers ]

The generator without, the frequency is stable i.e 50Hz. Under load the frequency raised up to 70Hz and coming back to 50Hz. The frequency is fluctuating like this. What is the reason behind it

Bryant Plus-80 gas furnace -- How can I increase the frequency of cycling? [ 1 Answers ]

-- currently the temperature swings are more than 5 degrees

How to increase 2.2kva generator output [ 2 Answers ]

How do I increase 2.2kva generator output and can I use electric motor on generators instead of petrol motors


View more questions Search