    Load bearing concrete floor beam support
    I had the misfortune of hiring an incompetent architect (and builder). One of the primary load bearing floor beams (20x45cm with 10 pcs 16mm rebar) ties into another lighter load bearing ring beam (20x40 cm with 6 pcs 12 mm rebar) mid-span. That is, there is no supporting column at the juncture of the two beams.

    These beams (among others) support a suspended reinforced concrete floor 10cm thick, and the larger beam spans a distance of 10 meters. It is unsupported except for a single supporting column at one end and the lighter ring beam it ties into, mid-span, at the other.

    I am sure it is only a matter of time before the lighter ring beam fails unless something is done to reinforce it. I presume it is possible to build a support column after the fact, but would like some expert advice on the best method to do this. If a column is added, what is the best way to tie it into the existing beam?
    dannac's Avatar
    dannac Posts: 267, Reputation: 9
    Full Member
     
    #2

    May 17, 2013, 04:59 AM
    How about a picture or sketch to better understand the setup.
    MH2's Avatar
    MH2 Posts: 15, Reputation: 1
    New Member
     
    #3

    May 17, 2013, 07:36 PM
    Hope this helps.
    Attached Images
  1. File Type: pdf Beam_work.pdf (11.5 KB, 162 views)
  2. dannac's Avatar
    dannac Posts: 267, Reputation: 9
    Full Member
     
    #4

    May 18, 2013, 03:20 AM
    MH2's Avatar
    MH2 Posts: 15, Reputation: 1
    New Member
     
    #5

    May 18, 2013, 07:14 PM
    About 30", maybe a bit more.
    dannac's Avatar
    dannac Posts: 267, Reputation: 9
    Full Member
     
    #6

    May 19, 2013, 10:27 AM
    If you have concerns, setup a temp support. Just set it back far enough that you have room to work on permanent support.

    2' x 2' concrete pad.
    3 - 8x8x8 or 8x8x16 cinder blocks.
    Couple pieces of 2 x 6 or 2 x 8.

    That should get you about where you need to be.
    If the 2 x blocks come up a little shy of the existing beam, cut a couple of wedges and drive between the 2 x blocks and existing beam.


Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What size beam do I need to clear span 30 ft and support a live load floor? [ 7 Answers ]

I am putting a storage loft in a shop/garage 30 wide by 36 feet long. The loft will be 12 feet by 30 feet across one end of the shop. I want work space under this loft so I am looking for a clear span, wall to wall of 30 feet. This beam will have to support a live load floor above it. Should the...

Max load bearing basement support post width using a beam [ 1 Answers ]

Purchased remolded home - want to finish basement - contractor repositioned the stairwell from top living area (ranch I level) -the old stair support posts were left in place.- problem is another post was added which made a triangle of post about 5 feet apart and not square to the room - this is...

Is a wall that runs beneath the support beam load bearing? [ 2 Answers ]

I have a house that was build in the late 30's and am working on finishing the basement. There is a wall that is directly beneath the wooden support beam and I want to add a large (6'-8') door to access the bedrooms. There is currently one small door in this wall. The beam and the wall run...

Question about support beam for load bearing wall [ 1 Answers ]

We are putting a 12x24' addition on the back our our house, making a large open room that measures 22x24' (1st floor only). My contractor says we will need a support beam that will span the 24' width of the house to support the second floor and a support pole placed somewhere along that beam. He...

Load bearing beam [ 2 Answers ]

Just wanting to know if I can build a load bearing beam out of three 11-7/8" 2x12's for a span of 10 feet. with a nail pattern of 4 nails on each side at every 12". Would this pass inspection?


View more questions Search