    Is a wall that runs beneath the support beam load bearing?
    I have a house that was build in the late 30's and am working on finishing the basement. There is a wall that is directly beneath the wooden support beam and I want to add a large (6'-8') door to access the bedrooms. There is currently one small door in this wall. The beam and the wall run perpendicular to the joists, which lead me to believe it may be load bearing. If it is, is creating a door way like this even possible and if so, what options do I have (if needed) to support the house?
    joypulv's Avatar
    joypulv Posts: 21,591, Reputation: 2941
    current pert
     
    #2

    Jul 25, 2012, 01:46 PM
    It surely sounds like a bearing wall.
    Any bearing wall can be taken out IF a big/strong enough beam replaces it, along with enough support at the ends to accept the load (several 2 x 4s as posts, (and sometimes even footings in the basement floor to carry the load further, such as in a large multi-story house). If it's a low beam already you can see about using a steel beam.
    You need to know the load of everything above the beam to be replaced, from the roof down and from the joists out. You can ask your building inspector or hire an engineer to calculate it (and the inspector might even require an engineer). If you feel you know a contractor with solid knowledge of loads you can ask him.
    Not to mention jacks to hold everything up while it's done.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Jul 25, 2012, 03:18 PM
    Is the wall separate from the beam or does the beam get spported by the wall? Are there any steel posts supporting the beam or just the wall? If it is indeed a bearing wall, and it seems so, you will need to support the beam by cribbing the joists on either side of the wall, determine the header size, I'd use a 2X12, and then install the header supported by 2X4's. 6-8 ft. is easily supported by 2X12's sandwiched with 1/2 ply. If you determine the wall is non load bearing, just cut the studs out but I would still add a header, maybe 2X6's.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Question about support beam for load bearing wall [ 1 Answers ]

We are putting a 12x24' addition on the back our our house, making a large open room that measures 22x24' (1st floor only). My contractor says we will need a support beam that will span the 24' width of the house to support the second floor and a support pole placed somewhere along that beam. He...

Beam size to replace load-bearing wall [ 13 Answers ]

Okay, I'm trying to decide if it's worth the trouble to open up a room in my basement. It is currently a 16 ft wide wall with a single doorway in it. It is a load-bearing wall. I'd like to open up the doorway to about 10'6" width. The wall supports the floor above, and there is another...

Grade beam or load bearing wall [ 2 Answers ]

I'm in the planning stage for our new house, and we're going with a permanent wood foundation. This is a full basement. I have two choices, I can go with your standard built up lumber grade beam for the house with teleposts (columns), or I can build a load bearing wall in the basement. ...

Replacing a load bearing wall with an engineered beam. [ 4 Answers ]

I have a load bearing wall between two living areas that I would like to remove to create one large space. I would like to do it without the beam exposed in the area. My question is can the ceiling joists be cut and reattached to the beam using joist hangers? I understand that there would have to...

Sizing a beam to replace load bearing wall. [ 3 Answers ]

I am planning on removing 15' of a 2x6 load bearing wall in my basement and want to confirm the sizing of the steel beam. I had an engineer have a look, but the only engineer available is a semi-retired fellow who sized the beam in exchange for having a couple of beers with him in the process. ...


View more questions Search