    How to replacing a manual reset high pressure switch on a ruud 2-1/2 ton heat pump
    How do you replace a ( P/N:47-21604-03) high pressure switch manual reset on a Rudd model:UPJA-036JAZ heat pump?
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Aug 7, 2012, 05:07 PM
    I would cantact Rudd to see if the fitting has a schrader valve. If it does, you simply untread the old limit, and thread a new one on. If there is no scrader valve, or the limit is brazed directly into place, you will need to reclaim the refrigerant, cut the old limit out, braze a new one in place, reclaim the system, and recharge. Hope you have a schrader valve connection. Good luck, and please let me know how things work out.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Do I have to remove freon to change high pressure switch on a heat pump? [ 2 Answers ]

High pressure switch stuck open how do I replace it.

How do you change a high pressure safety switch on a luxaire heat pump [ 1 Answers ]

High pressure safety switch has yellow wires and apprears to be soldered on. Is that possible or does it come off without removing charge.

What is the correct suction pressure and head pressure for a 3 ton tempstar heat pump [ 1 Answers ]

When the yellow jacket brand gauges are put on a 3 ton Tempstar heat pump what should the correct suction pressure and head pressure be. I suspect it to be overcharged in freon. Because it is freezing the compressor, accumulator tank and all the lines soild ice.

2008 4 ton Goodman heat pump doesn't switch into electric strip heat? [ 18 Answers ]

OK even when its 17*F out I can still here it running at night. So is this a problem? I mean it runs non stop.

Amana Heat pump High pressure switch tripping [ 19 Answers ]

Called tech found unit pressure switch tripped, reset added freon. Lasted less than a week. Appears tripped again. He mentioned fan could be the culprit when he was out. Is there a way to eliminate this as a cause? Any other possible solutions? Brand new filter in unit after first episode.


View more questions Search