    Heil Furnace Troubleshooting
    I have a Heil FBF100F14G1. The pressure tube for the inducer motor gets condensate in it and quits heating. After draining the water it heats again until next time. What causes this problem? Improper venting?
    Thanks, Keith
    TopTechnician's Avatar
    TopTechnician Posts: 9, Reputation: 1
    New Member
     
    #2

    Jul 28, 2012, 07:53 PM
    It could be that you don't have a trap on the furnace drain. Most condensing furnaces have special traps that come with the furnace. The trap prevents the suction of the inducer from pulling water back up the drain pipe. Your trap could be cracked or missing.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heil n8mpn furnace troubleshooting? [ 11 Answers ]

Heil N8MPN. Fires up properly. Shuts down circulating fan and burners after 15 seconds to several minutes. Draft inducer continues to run for short period, kicks out then immediately kicks back on and then unit goes back through same sequence. Honeywell valve shows proper function with heartbeat...

Heil Furnace Troubleshooting [ 1 Answers ]

Heil furnace no ac the transformer has been replaced twice keeps burning out

Heil Furnace Troubleshooting? [ 0 Answers ]

My heil furnace won't start up, no gas coming out of control valve so igniter doesn't work, replaced valve and still nothing, exhaust fan works however

Heil furnace troubleshooting [ 1 Answers ]

Have a heil 100,00 BTU furnace that is when it gets cold at night the burners will not stay burning, the electric pilot light is on but no ignition of the burners unless I shut the system down for a while. The blower stays blowing with no ignition of the ports


View more questions Search