    Repco boiler model #LA150c pressue in boiler too high
    Pressure rellief valvue was replaces a year ago for laking. Water pressue still reaching 40psi? Don't know why shoud be 30psi.. water still leaking off from the pressure relief valvue. I've tried to beeed oof water from the pressure relief valvue and the drain with n help. Pressuet still moves ut to 40psi. What should I be looking for?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jul 18, 2012, 12:39 PM
    Quote Originally Posted by pfrouge View Post
    Pressure rellief valvue was replaces a year ago for laking. Water pressue still reaching 40psi ?? don,t know why shoud be 30psi.. water still leaking off from the pressure relief valvue. I've tried to beeed oof water from the pressure relief valvue and the drain with n help. pressuet still moves ut to 40psi. What should i be looking for?
    Your expansion tank is full of water so the water when it gets hot cannot expand into a full of water tank space. Secure boiler water fill valve and drain expansion tank. IF you have the bladder type tank you will have to replace it since the bladder is ruptured internally and cannot be repaired.

    The water pressure valve could also be defective along with the tank.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Repco hot water boiler [ 2 Answers ]

What is the age of Repco gas-fired hot water boiler LA100C#18316592? Thank you.

Spark ignition gas boiler Weil McLain pilot lights but boiler doesn't s [ 2 Answers ]

Spark ignition gas boiler. Weil McLain gas boiler. The pilot lights but the boiler doesn't start.

Repco boiler age [ 0 Answers ]

Trying to determine the age of my repco boiler (model# LA150L, serial# 184-2579). Not sure if it was manufactured in Jan of 1984 or the 25th week of 1979. Any idea?

Is my hobart 600 a steam boiler or a hot water boiler. There is no circulator pump [ 0 Answers ]

I have a Hobart 600 automatic gas fired furnace. The first thing is I cannot see a circulater pump or a air tank. I can not tell if it is steam or hot water. When I go to fill the system with water, the system fills and then the water continues to flow out to the drain pipe.

Repco boiler pilot lighting instructions [ 0 Answers ]

There is no heat or flame to the boiler, I tried to light it with the pilot switch, but it is not lighting.is there another way to light the pilot?


View more questions Search