    Spark ignition gas boiler Weil McLain pilot lights but boiler doesn't s
    Spark ignition gas boiler. Weil McLain gas boiler. The pilot lights but the boiler doesn't start.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Oct 27, 2011, 04:32 PM
    When the pilot lights, does the spark ignition keep sparking, or does it quit? If it keeps sparking even when pilot is lit, you may have a dirty or defective flame senser, or bad ignition control. If the spark quits, but the main burners don't kick in, check for power to the gas valve. Also check all limits to make sure they are closed. What model is your Weil Mclain?
    llyddc's Avatar
    llyddc Posts: 3, Reputation: 1
    New Member
     
    #3

    Oct 27, 2011, 05:35 PM
    CG-8-PIDN

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Weil mclain boiler problems? [ 3 Answers ]

I would like to know why Weill McLain does not stand behind their products. We purchased a Ultra 230 Boiler in October 2009 and a Ultra Plus 80 Water Heater at the same time at a cost of $8302.66. Hooked both up and moved into our house in November 2009. The boiler stopped working April 9, 2010,...

Weil mclain ultra boiler [ 3 Answers ]

I have a Ultra 155 boiler with an indirect 40 gal DWH. 4 zones, plus prioritized domestic water Taco switching relay. The system uses 4 taco cartridge circulators for the four zones plus one for the DWH. It constantly goes off (at least once every other week in the winter) on a too much flow...

Transformer for Weil Mclain e.g. Boiler [ 7 Answers ]

I'm looking for a transformer with a circuit breaker to replace a White-Rodgers 90-112 transformer/relay. I can't find the combination with a breaker so I figured I'll buy the transformer and then pop it in in the 4" X 4" backplate since the relay is not used anyway. Will the Honeywell AT150F1022...

Weil McLain Gas Heat & Hot Water Boiler [ 1 Answers ]

What does error code E-19 mean?

Weil-McLain Boiler settings? Look right? [ 3 Answers ]

Weil-McLain Gold Oil Model: WTGO-4 Series: 3 Net Output... Water 128 MBH Pressure set at 22 Water Temp at 162 Feet H20 at 40 Water Heater is Amtrol Boilermate WH7ZDW


View more questions Search