    Elevctric welder breaker requirements
    I have an 230 VAC Forney arc welder. The spec plate shows "Input amps Max R.L.---32" and "Input amps S.C.-----48". What circuit breaker do I need? Would a 30 amp double pole be enough?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Feb 11, 2012, 05:41 AM
    What model number welder do you have?

    Does the welder have a cord and plug provided? What amp rating is on the plug?
    List all nameplate details.
    rabeltz's Avatar
    rabeltz Posts: 4, Reputation: 0
    New Member
     
    #3

    Feb 11, 2012, 10:44 AM
    It is an old Forney Model C-5 welder. Maximum output is 180 amps. It has a 50 amp 230VAC plug. The following is on the label. Model C-5, Pri Volts 230, Freq 60, Phase 1, Volts at max. output--25, Max. open circuit volts----75, Rated duty cycle--20%, Input amps at max.R.L.---32, Input amps S.C.--48, Power Factor at max R.L.---80%, Max Sec. Amps---180. I have had a 40 amp breaker and it worked okay, but I need to change the service panel and I thought that I should put in the proper breaker.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Feb 11, 2012, 01:15 PM
    Input amps is relative to the current used to weld, if thin metal then a 30 or 40 will be enough, if there is any chance the unit could be used heavier output amps , then use the 50 amp circuit,
    rabeltz's Avatar
    rabeltz Posts: 4, Reputation: 0
    New Member
     
    #5

    Feb 12, 2012, 10:14 AM
    Thanks, That answers my question. I'll probably go with 50 amps to cover all possibilities.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Br220 breaker: 208/230 welder [ 5 Answers ]

At the service panel, I have a Cuttler Hammer BR220. The assigned receptacle is a twist-loc 250V 20A type (NEMA LS 20-R). The welder I want to use is a Tri-Arc 160 which is rated for 208/230. This plug does not match the wall receptacle. What is the path of least resistance to turn...

Wiring a welder [ 3 Answers ]

I have a quick question about hooking up a welder. Lincoln 225/125 AC DC with a 3-prong plug. I am using 8-3wire, can I use the white wire as my ground in the panel and can I also use the bare wire connected to an anchor screw in the plug to the same ground connection in my panel? Thanks, Dale

115v arc welder tripping 20amp breaker [ 2 Answers ]

I just bought a Arc Welder that can use 220 or 115 but since the only 220v outlet is the dryer inside the house I had to choose the 115v mode. I have it plugged in inside the garage on a 20 amp breaker. The manual said no to go above 70v on a 30 amp breaker. The job I need requires all 70v and when...

Welder [ 1 Answers ]

I found an old lincoln welder that I can't identify. I guess it looks like a water tank about 4 feet tall and 3 feet wide with a crank on the side. Ring any bells


View more questions Search