    Esab 150 miniarc welder kicks 20 amp breaker on 110v when I get up around 100 amps
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Oct 13, 2010, 08:46 AM

    Read your question please!

    Your 20 amp breaker is opening when it sees a sustained 100 amps. Thank you, to the breaker company for protecting you.

    Is your welder supposed to be connected via a 20 amp breaker? If it is, are you sure that you have the proper type breaker for use with the welder.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Oct 13, 2010, 08:55 AM

    FYI - Additional information:

    (I do realize that you are talking about the 100 Amp Output of the welder. You need to put an ammeter on the conductors feeding the welder to make sure that the breaker is seeing the correct amperage. Per the inputs (highlighted in red below, I would have chosen to use a 25 or 30 (see NEC 240.6 - you can link to it above.) amp breaker. What did the installation instructions call for?)


    Specifications
    Primary Input Voltage/Phase: 115/208/230 vac, 1 ph, 50/60 Hz
    Voltage Tolerance: +/- 10%

    115V Operating Data
    - Output Range (Stick): 5A/20V to 85A/23.5V
    - Stick Duty Cycle & Rated Output: 100% - 85A @ 23.4V
    - Output Range (TIG): 5A/20V to 100A/14V
    - TIG Duty Cycle & Rated Output: 100% - 100A @ 14.0V
    - TIG Duty Cycle & Rated Output: 60% - 130A @ 15.0V
    - Primary Input Current @ 100% Duty Cycle: 19A
    - Primary Input Current @ 60% Duty Cycle: 26A
    - Open Circuit Voltage (max): 83 V

    230V Operating Data:
    - Output Range: 5A/20V to 150A/26V
    - Stick Duty Cycle: 110A/24.5V @ 100%, 140A/25.6V @ 60%
    - TIG Duty Cycle: 110A/14.5V @ 100%, 150A/16V @ 60%
    - Primary Input Current @ 100% Duty Cycle: 17A
    - Primary Input Current @ 60% Duty Cycle: 23A
    - Open Circuit Voltage (max): 83V

    Net Weight: 18 lbs
    W 5.75 in x L 15 in x H 11 in

    Comes Complete With:
    - Power Source
    - 10 ft. Work cable & Clamp
    - 10 ft. welding cable w/electrode holder
    - 1# 6013LV electrodes
    - Plastic carrying case

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can a 150 amp meter panal handel a 100 amp, 40 amp, 30 amp and 30 amp brakers. [ 2 Answers ]

My meter panal is a 150amp panal. I have a 60 amp sub panal coming off it a 30amp to my stove a 30 to dryer and a 40 to the a/c. i want to upgrade the 60 amp sub panal to a 100 amp panal. Will the 150 amp meter panal handel it or do i need to have a 200 amp meter panal installed

Can I put a 150 amp breaker in a 200 amp panel to feed a 150 amp sub panel? [ 8 Answers ]

Can I put a 150 amp breaker in a 200 amp panel to feed a 150 amp sub panel with a 200 amp service?

Pulling 100 amps of main 200 amp service [ 9 Answers ]

I'm pulling 100 amps off my main house 200 amp service to my new Garage. It is an indoor run of 70 feet. What size wire do I need? Copper or Aluminum? How many conductors? If I run it in the joist space do I need to case it? Thanks Ron

100 Amp panel vs 325 Amps worth of breakers? [ 1 Answers ]

I have a house built in '49. The basement was remodeled by previous owner and the Service Panel was upgraded to 100 AMP. The wiring to the breakers are a mixture of modern sheathed 3 wire for the basement level and the original knob and tube wiring for main floor circuits (all fed via the attic)....

Finding a heavy duty 100 (or 150 Amps) plug and receptacle [ 1 Answers ]

Hi, I'm trying to find a 100 or 150 amps heavy duty plug and receptacle (and box) that will be used outdoors (thus needs to be water tight or water resistant). I've found all of them from Hubbell, but this is not cheap. Anyone knows of an alternative? This is to hook up a mobile cabin that will...


View more questions Search