    At the service panel, I have a Cuttler Hammer BR220.

    The assigned receptacle is a twist-loc 250V 20A type (NEMA LS 20-R).

    The welder I want to use is a Tri-Arc 160 which is rated for 208/230. This plug does not match the wall receptacle.

    What is the path of least resistance to turn this into a compatible power chain?


    Thanks,
    Kalo :confused:
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    May 10, 2009, 07:34 AM
    What plug is on the welder cord?
    What are the INPUT specs of the welder?

    If it is a 160A output welder the input amps will likely be much higher than a 20A circuit will provide.
    MachineMonkey's Avatar
    MachineMonkey Posts: 3, Reputation: 1
    New Member
     
    #3

    May 10, 2009, 08:53 AM
    Quote Originally Posted by stanfortyman View Post
    What plug is on the welder cord?

    I don't have the welder in front of me, but I'd describe it as being visually similar to the American house plug while being twice it's size (or thereabouts). It has 2 spade contacts and a round ground post. The spades are either parallel or perpendicular to one another, not inline.

    What are the INPUT specs of the welder?

    Not certain. Googling doesn't give me much (it was remarketed as an Airco Dipstick 160). I did find this at a Hobert forum, though:

    "Input is 230V 60 amps for stick and 30 amps for MIG."



    If it is a 160A output welder the input amps will likely be much higher than a 20A circuit will provide.
    So, I'll need to change the breaker to something with a higher amperage rating for a start. The receptacle, I'd change at the same time, I guess.

    Can I change/upgrade circuit breakers without bringing PG&E into it?

    Thanks


    My house service panel has a main of 200A, so that's OK.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    May 10, 2009, 09:40 AM
    Quote Originally Posted by MachineMonkey View Post
    So, I'll need to change the breaker to something with a higher amperage rating for a start. The receptacle, I'd change at the same time, I guess.
    NO!! You cannot simply change the breaker and receptacle and use the same wire. This should be obvious.
    You are a welder. What happens if you use a 3/32" rod at 180 amps? The same thing will happen to the wire in the wall if you run too many amps through it.
    The wire in the wall is rated at 15 or 20 amps. You need a 50A circuit.




    Quote Originally Posted by MachineMonkey View Post
    Can I change/upgrade circuit breakers without bringing PG&E into it?
    Certainly, but like I am saying, it is far more than that.
    You need to run a new larger circuit to this welder. As I suspected it will require a 50 or 60 amp circuit run with #6cu wire. Typically we would use 6/2NM cable.
    The plug you describe is a standard 250v/50a plug used on many welders.
    MachineMonkey's Avatar
    MachineMonkey Posts: 3, Reputation: 1
    New Member
     
    #5

    May 10, 2009, 09:57 AM
    Quote Originally Posted by stanfortyman View Post
    NO!! You cannot simply change the breaker and receptacle and use the same wire. This should be obvious.
    You are a welder. What happens if you use a 3/32" rod at 180 amps? The same thing will happen to the wire in the wall if you run too many amps through it.
    The wire in the wall is rated at 15 or 20 amps. You need a 50A circuit.

    Got it.


    Certainly, but like I am saying, it is far more than that.
    You need to run a new larger circuit to this welder. As I suspected it will require a 50 or 60 amp circuit run with #6cu wire. Typically we would use 6/2NM cable.
    The plug you describe is a standard 250v/50a plug used on many welders.
    So, I need to have an electrician run new wire from the service panel to the existing receptacle (or new receptacle, if a new circuit run is easier or beneficial).


    Thanks again.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    May 10, 2009, 10:04 AM
    Exactly. Very good choice. :)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Gfci breaker + outlet in same circuit.breaker tripping [ 4 Answers ]

I have a gfci breaker for a bathroom and there is an additional gfci outlet in the bathroom on the same circuit. The breaker was tripping intermittently over the past week and now will not re-engage. Should I suspect a faulty breaker or is it better to troubleshoot the circuit first? The...

How do I determine breaker amps on a 240v double breaker? [ 7 Answers ]

Hi, I have a new elec. Cooktop that needs 240V, 40 amps. Each pole of the double pole breaker for my cooktop circuit Says 30amps. So can this 240v circuit support 60 amps, or just 30? Thanks!

Bathroom GFI outlet trips breaker at breaker panel [ 2 Answers ]

Hello all. Our house is approximately 13 years old. Each morning when both the iron and blow dryer is plugged into two separate GFI outlets in the master bathroom, the circuit will trip the 15 amp breaker in the breaker panel. Is it possible to upgrade the breaker to a 20 amp without...

115v arc welder tripping 20amp breaker [ 2 Answers ]

I just bought a Arc Welder that can use 220 or 115 but since the only 220v outlet is the dryer inside the house I had to choose the 115v mode. I have it plugged in inside the garage on a 20 amp breaker. The manual said no to go above 70v on a 30 amp breaker. The job I need requires all 70v and when...

Welder [ 1 Answers ]

I found an old lincoln welder that I can't identify. I guess it looks like a water tank about 4 feet tall and 3 feet wide with a crank on the side. Ring any bells


View more questions Search