    Subpanel added to main disconnect box below meter?
    I have a 400 amp meter base and 2oo amp service panel. The house is 7 years old and it was only a few hundred more for the meter base so I went for it. My question is; below the meter is a box with a 200 Amp disconnect and room to add additional breakers. Can I add a sub panel in my barn connected to a 100 amp breaker in this box?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 12, 2012, 06:01 AM
    You may have a 400 amp meter socket, need to be sure you have a 400 Amp incoming service service the meter and disconnects.

    If so, then sure, and the 100 Amp feeder for the barn.
    BSTEVEN's Avatar
    BSTEVEN Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 12, 2012, 05:17 PM
    Sub-panel added to main disconnect box below meter.
    Thank you for the response Tkrussell. Today I talked with my electric company and found that, although I have a 400 amp meter base, I only have a 200 amp meter. Can I still add a breaker to this box for the sub-panel I would like in my barn?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jan 13, 2012, 03:35 AM
    Depends on the existing load, and if the 200 Amp service can handle the additional load.

    Need to have a service rating load calculation done to confirm.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

200 amp outside meter box with disconnect [ 1 Answers ]

I am installing a new service upgrade from 100 amp to 200 amp my breaker box is 30 feet away from the meter box. Is the meter box fused after the meter to the breaker box or is it a pull switched

Wiring from meter box to main lug [ 1 Answers ]

I have Cutler-Hammer 200 Amp. Meter box with additional spaces in the bottom portion and I want to run 100 Amp. Service to a building. I am looking for how-to tips and diagrams to accomplish this.

How many feet of wire between main breaker and meter base without a disconnect [ 1 Answers ]

What is the code for the length of wire between the panel box and meter base without installing a disconnect

Wiring a combination meter and main disconnect. [ 1 Answers ]

I bought a Square D CQRA200 Meter/main disconnect combination and I expected to see the neutral isolated from the ground. Does the neutral and ground start from the same block?

Can the CB in a subpanel exceed the ampacity of the CB in the Main Disconnect? [ 3 Answers ]

Can the main breaker in a sub panel exceed the ampacity of main breaker in the primary disconnect?


View more questions Search