    Bryant 3/4 hp blower start up problems... runs OK.
    I have a bryant 3/4 hp blower running at 15.34 or so amps. Is that correct. The blower runs OK if I leave it running. If I turn it off, I need to spin the drum to get it to move again. Is this a problem with the capacitor or the motor? Any advice...
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    Sep 23, 2011, 06:22 PM
    I would start with the run capacitor. A bad run capacitor will make it have high amps and hard to start. Kill the power going to the system and remove the run capacitor and take it to a local hvac dealer to have it tested. If it test bad you get off buying a cheap part.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bryant Plus 90 blower runs intermittently [ 7 Answers ]

I have a Bryant 90 Plus (350 MAV) gas furnace that is about 13 years old with an intermittent problem. The inducer motor starts, igniter lights, gas valve opens, and burner lights and runs but occasionally the blower motor will not start. When this occurs the plenum attached to the furnace gets...

Bryant furnace model 310AAV/JAV blower runs continue [ 0 Answers ]

Bryant furnace model 310AAV/JAV the blow run continue. Even disconnected from the thermostat

Blower runs constanty, AC is cooling. Will this cause other problems? [ 1 Answers ]

I have a 17 year old Janitrol furnace/AC. It was cooling properly, but the blower on the furnace was running almost constantly. Had service and the thermostat was changed. Continued to have the same problem even after a new thermostat (its set on auto) until it stopped cooling. Had service and had...

Bryant Furnace Blower Motor Problems [ 1 Answers ]

I have a Bryant 80 furnace. As louck would have it the blower motor just went and of course it is within a year of the warranty expriing. Does this seem right?

Bryant Plus 80 Code 33 any ideas? Blower runs all time! [ 2 Answers ]

I have a Bryant Plus 80model 395cav048135 that runs for about 10 minutes (blows heat etc) then flames shut off but fan runs continusly till reignites and heats again. (aprox 10-15 minutes) have tried researching this am but no definte answers any ideas?:)


View more questions Search