    On 208/230 3phase is it OK to have 70 volts to ground on L1 on L2 130 on L3 129
    On 3 phase 208/230 power is it OK to have 70 volts to ground on L1,on L2 130 and on L3 129
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 6, 2011, 04:10 AM
    No, all three phases should read 120 volts +/- .on a 120/208 volt 3 phase 4 wire WYE system.

    The 129 and 130 volt readings are a bit high, and may be due to high voltage from utility or the incorrect taps are being used on a distribution transformer.

    The 70 volts indicates a problem with that phase, poor connection, failed transformer, etc.
    sinnadurai's Avatar
    sinnadurai Posts: 127, Reputation: 2
    Junior Member
     
    #3

    Aug 7, 2011, 07:07 AM
    Switch off the load and check L1L2,L2L3,L3L1,L1N,L2N and L3N. If they are balanced your problem is the load.
    Newton1Law's Avatar
    Newton1Law Posts: 60, Reputation: 5
    Junior Member
     
    #4

    Aug 14, 2011, 07:23 AM
    I can not say I am familiar with a 208/230 volt system, however, if it is a 120/208 volt system, the readings you have measured suggests that the system is a 120/208 ungrounded Wye or Y system. One phase is partially connected to a common point of the "Y" and the displacement of you're the phases at at105 degrees, 107 degrees and 149 degrees, approximately, will give you the voltages you have read. The only way this could be sustained on a 4 wire Wye system is if there is no ground connected to the neutral point of the Wye, or you have a bad or broken connection. Repair of this connection will however caused the faulted phase (@70 volts) to blow a fuse or burn open. Pleae have an electrican work with you on this or contact the local utility if these voltages are found on the incomming service.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to wire a 208 /230 volt supply for a welder? [ 7 Answers ]

To Whom It May Concern: I need some advice on a 4 3 wire with ground wire; where does the ground wire go on a 208/230 setup? I am using a 50 amp double pole breaker. Sincerely, Tracy G. McDougal [email protected]

Can I run a 208-230 volts 1/3hp 60hz, model no ka55hfxcl-240 nfg k91c on a 110 or [ 3 Answers ]

I have a mobel home furnace blower motor that is a 208-230 volts I want the motor to run on a 120 if I can , it has four wires red,black orange and brown thank you

What kind of ground screw to use for grounding w a 4-6 gauge wire from a 208/230 volt [ 2 Answers ]

I am wiring a receptacle for a millermatic 251 welder that requires 48/42 amps. I am using 4 gauge wire for the two hots. Little overkill but it was gotten for free. I am not sure how to ground the 4-6 gauge wire I plan on using on the receptacle. The typical grounding screw meant to be screwed...

Br220 breaker: 208/230 welder [ 5 Answers ]

At the service panel, I have a Cuttler Hammer BR220. The assigned receptacle is a twist-loc 250V 20A type (NEMA LS 20-R). The welder I want to use is a Tri-Arc 160 which is rated for 208/230. This plug does not match the wall receptacle. What is the path of least resistance to turn...

208/230 A/C Trouble [ 7 Answers ]

I just bought a used, "through the wall" air conditioner. The unit is 208/230V with 6.5/6.9 Amps. The plug for the AC unit, however, is a three-prong (B) plug with one circular (ground) and two horizontal prongs (unlike the normal B plug with two vertical prong next to each other) and does not fit...


View more questions Search