    Ruud Seer 11 condenser fan 1/6 hp- .90A-1075rpm replace with 1/5hp-1.3A-1075rpm?
    Hello,
    I am wondering if I can replace the condenser fan motor on a Ruud Seer 11
    [1/6hp-.90A-1075rpm-208-230V]
    With a motor from a slightly larger Ruud unit (possibly seer 12?)
    [1/5hp- 1.3A-1075rpm-208-230V]
    Do I need to replace the capacitor with the one that goes with the larger hp motor?
    (or do they use the same one, for both motors?)
    Thank you for your help,
    Jason
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #2

    Jun 21, 2011, 01:13 PM
    The HP is different but the RPM`s are the same,, you probably can get by,, the capacitor has to match the larger hp motor that you are going to use, label on side of motor should tell you the size cap you need. Hold on to the 1/6 hp motor so you will have the original to match up if/when you need to replace again.
    Make sure direction of rotation is correct on the bigger motor
    jasoni's Avatar
    jasoni Posts: 3, Reputation: 1
    New Member
     
    #3

    Jun 22, 2011, 07:10 AM
    Comment on wmproop's post
    Thank you for your quick response, I will try the switch and post my results, but first I have to change the breaker, it keeps tripping and I know the condenser fan was pulling/dragging on start up (and now does not start at all), but want to rule out a bad breaker first. Then I will make the condenser fan motor switch, and hopefully all cool after that.
    Thanks again,
    Jason
    jasoni's Avatar
    jasoni Posts: 3, Reputation: 1
    New Member
     
    #4

    Jun 27, 2011, 09:35 AM
    Comment on wmproop's post
    Okay, changed the breaker, and the unit tries to start, - condenser fan hums/buzzes and spins slowly (very), then after approx 1 min. breaker trips. So I think either the condenser fan motor or the capacitor is shot, will be replacing with the other 1/5 hp motor and matching capacitor. Hopefully that will fix my issue. I will post my results.
    Jason
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #5

    Jun 27, 2011, 06:24 PM

    Hey jasoni, just one thing to try. Capacitors are cheap, so I would suggest taking the current capacitor to an electrical shop and having them test it for you. Your issue may only be a bad cap. Worth a shot. If cap proves good, then new motor and matching cap it is. Also, make sure you have correct voltage to the fan motor.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can uReplace a 10 seer ac condenser w/a 13 seer w/o changing the inside 10 seer unit [ 8 Answers ]

We have a 10 seer 2.5 ton heat pump outside condensing ac unit, that sprung a leak that cannot be repaired. We have had 5 repairmen come out and look. 3 of them say we have to replace the inside 10 seer 2.5 ton compressor and furnace as well. 1 of the 5 says we can just replace the outside unit...

10 seer condenser and 13 seer evaporator [ 3 Answers ]

If you put a new 13 seer fan coil in a system and keep the 10 seer condencer outside will this still balance out or will it cause execive compresser wear and cause a burn out?

Can I buy a new AC compressor for my 13 yr old Ruud Seer !0? [ 1 Answers ]

I am told my compressor is nearly done, and were I to buy a new one, as of two months ago, it would be unlike the one I have, and I would have to replace lines into my house and much more, and after doing all that I would still be left with a 13 yr old furnace, so I am told I should just spend $5K...

Ruud 10 seer A/C unit not working 10y/o [ 1 Answers ]

Ruud 10 seer ac new wire, new capasitor, new fan motor, Hard start kit on unit , & new thermastat The unit starts and runs for about 5 minutes the fan motor stops the compressor kicks on and runs then when the fan stops running it is dead. Help This unit is about 10 years old. Why will it not run??

Replace RUUD Air Handler 10 Seer [ 4 Answers ]

I have a six year old Ruud Heat Pump (10 seer) with an air handler in the attic. The compressor on the heat pump failed and I had it replaced. The space was still not being cooled. I suspect that the coil in the air handler is clogged. It will cost $300 to clean and is not a guaranteed fix. ...


View more questions Search