Ruud Seer 11 condenser fan 1/6 hp- .90A-1075rpm replace with 1/5hp-1.3A-1075rpm?
Hello,
I am wondering if I can replace the condenser fan motor on a Ruud Seer 11
[1/6hp-.90A-1075rpm-208-230V]
With a motor from a slightly larger Ruud unit (possibly seer 12?)
[1/5hp- 1.3A-1075rpm-208-230V]
Do I need to replace the capacitor with the one that goes with the larger hp motor?
(or do they use the same one, for both motors?)
Thank you for your help,
Jason
Comment on wmproop's post
Thank you for your quick response, I will try the switch and post my results, but first I have to change the breaker, it keeps tripping and I know the condenser fan was pulling/dragging on start up (and now does not start at all), but want to rule out a bad breaker first. Then I will make the condenser fan motor switch, and hopefully all cool after that.
Thanks again,
Jason
Comment on wmproop's post
Okay, changed the breaker, and the unit tries to start, - condenser fan hums/buzzes and spins slowly (very), then after approx 1 min. breaker trips. So I think either the condenser fan motor or the capacitor is shot, will be replacing with the other 1/5 hp motor and matching capacitor. Hopefully that will fix my issue. I will post my results.
Jason