Microwave trips breaker.
Dedicated circuit. Replaced 15A breaker w/20A. Replaced outlet with HD 20A. Still trips. Ran HD extension cord to a different 15A outlet. Works perfectly. I am out of guesses.
|
|
|
 |
Printers & Electronics Expert
|
|
Jan 6, 2011, 10:02 AM
|
|
|
First, you have created a dangerous code violation if you just changed the breaker and receptacle. A 20 amp circuit must use a #12 AWG copper cable or a #10 AWG aluminum cable. Not a #14 AWG copper cable or a
After this error is correct I would next verify that the circuit is actually a dedicated circuit. Sounds to like it is not. Next, make sure the connections are tight. Loose connections create heat which creates fire.
Most microwaves that I have installed required a 20 amp circuit as does the counter top appliance circuits in the kitchen.
Using 20 amps on a #14 AWG copper cable is a FIRE waiting to happen.
|
|
|
 |
New Member
|
|
Jan 6, 2011, 10:11 AM
|
|
|
Comment on donf's post
I am aware of that. I know code, I built the house. It is a dedicated circuit. The Westinghouse microwave is 3 yrs old and works perfectly with the extension cord plugged into a wall outlet. The owners manual states that it needs a 15A circuit.
|
|
|
 |
New Member
|
|
Jan 6, 2011, 10:15 AM
|
|
|
Comment on donf's post
Wires on new outlet are wrapped on the screws, no push ins. Connections are very tight. Double checked that.
Still don't know why it trips a 20A breaker on the dedicated circuit but not on the other 15A circuit. Gremlins?
|
|
|
 |
Printers & Electronics Expert
|
|
Jan 6, 2011, 10:28 AM
|
|
|
Please do not use the "Comment" section to return information. Please use the "Answer this question" block.
Sorry, but I do not know what level of experience and knowledge of code you have. And you did not let us know.
There is no logical reason why a microwave that requires a 15 amp circuit, trips the circuit. That said, if you verified the correct operation of the circuit, then the problem may be the microwave.
How did you verify the correct operation of the circuit? Did you use a Multi meter or a Amperage tester?
As you already know, a microwave is not to be run an extension cord.
I still come back to the circuit in question, especially since you say that the microwave works on a multi use 15 amp line.
|
|
|
 |
current pert
|
|
Jan 6, 2011, 10:50 AM
|
|
|
Does it trip if you try say a toaster there?
|
|
|
 |
New Member
|
|
Jan 6, 2011, 11:18 AM
|
|
|
The extension cord in question is a 10' 30A which I normally use for my 5HP compressor. I think it is quite adequate.
I plugged the microwave back into its dedicated circuit a bit ago and it is working properly so I put the 15A breaker back in. If it pops again, I'll try the toaster oven on that outlet.
This is just weird. I also suspected the unit but it functioned perfectly on the other outlet.
I guess I'll have to take a wait and see stance here. I'm telling you, there is a gremlin here :) If all else fails, I'll drop a #12 to the basement and put it on a new 20A circuit on that panel.
Thank you for the response. I'll keep you posted.
|
|
|
 |
Printers & Electronics Expert
|
|
Jan 6, 2011, 11:41 AM
|
|
|
Since we are into the weird world, did you check to see that there are no high amperage cables adjacent to the microwave cable and inducing a signal into the cable?
|
|
|
 |
New Member
|
|
Jan 6, 2011, 12:30 PM
|
|
|
Interesting. But the main line comes up from the basement and the MW circuit line runs up through the ceiling and over 20' to the unit which is an over-stove. It does cross over the mains inside the panel.
|
|
|
 |
New Member
|
|
Jan 6, 2011, 12:53 PM
|
|
|
I don't believe in ghosts. But I may change my mind. Today, the element went out in the dishwasher. My wife just informed me that the dryer element burned out. And the water heater is tripping its internal breaker daily.
I'm moving...
|
|
|
 |
Uber Member
|
|
Jan 6, 2011, 01:09 PM
|
|
|
Before calling Ghost Busters, I would be calling in a qualified service electrician to troubleshoot your system, to include the utility feed.
Could be a loose connection in the neutral, or something similar with the live feeds, to be causing the recent rash of damaged appliances and tripping breakers.
|
|
|
 |
Ultra Member
|
|
Jan 6, 2011, 07:02 PM
|
|
|
I think it was explained when you said "I built the house"
|
|
|
 |
New Member
|
|
Jan 13, 2011, 02:16 PM
|
|
|
I would check all the incoming main line connections, since it is all over many different devices. It may be in the panel ,the meterbase or the actual feeder drops at the mast. Usually you have to call your utility provider to ck the mast and the meterbase since they don't allow you to break their tamper tag.Good luck.
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Bathroom GFI outlet trips breaker at breaker panel
[ 2 Answers ]
Hello all. Our house is approximately 13 years old. Each morning when both the iron and blow dryer is plugged into two separate GFI outlets in the master bathroom, the circuit will trip the 15 amp breaker in the breaker panel.
Is it possible to upgrade the breaker to a 20 amp without...
Microwave trips circuit breaker
[ 1 Answers ]
Please help - I'm stumped. I have a swimming pool pump, and an electric kettle all working off a 20 amp CB. The pool pump and the electric kettle will work together but not the pool pump and the microwave. The wattage of the electric kettle is 1500 and the microwave is 1100. If the amps are...
New 15A breaker trips main 100A breaker
[ 6 Answers ]
Hi,
I've been finishing my basement and I added a few 15A breakers
One room has 8 outlets in series with the first starting about 6 feet from the main panel. There is currently no load on this outlets.
When installing the drywall I accidentally shorted the outlet closest to the panel. It...