    mdmaynard's Avatar
    mdmaynard Posts: 40, Reputation: 1
    Junior Member
     
    #1

    Dec 21, 2010, 09:49 AM
    Thermostat for baseboard heaters
    I am trying to find out the wattage the following thermostat will handle:

    Honewell CT410B

    I just bought to feed three baseboard heaters with a total wattage 3500 watts. Want to make sure this will work without overloading Thermostat

    Also if Thermostat were overloaded and breaker did not trip what would happened would the line side wires melt or the load side wires melt?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 21, 2010, 10:11 AM

    Beats the hell out of me what this stat is rated, there are no electrical specs to be found at Honeywell either:

    http://yourhome.honeywell.com/home/A...archkey=CT410B

    Which I find very odd that no load rating is published.

    You need to contact Home Depot and/or Honeywell to confirm what load this device can handle.

    An overload condition on a device that would not exceed the circuit breaker rating can result in fire, not just melted wires.
    mdmaynard's Avatar
    mdmaynard Posts: 40, Reputation: 1
    Junior Member
     
    #3

    Dec 21, 2010, 10:21 AM

    The paperwork that came with Thermostat does not say either.

    I ask the overload question because the thermostat I am replacing had some problems. When I pulled it out the to line side wires were melted together and the wire nuts were melted together. However the load side wires were just fine.

    I am replacing the breaker as the breaker never tripped. But I want to know what caused this to happen to begin with.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Dec 21, 2010, 10:30 AM

    I would suspect loose connections, or a poorly made stat.

    Electric heat is a sizable load, and can fatigue devices.
    mdmaynard's Avatar
    mdmaynard Posts: 40, Reputation: 1
    Junior Member
     
    #5

    Dec 21, 2010, 10:34 AM

    If it was bad thermostat wouldn't the thermostat be burnt up? Just asking as I want to figure this out.

    I really need to find out the load rating of thermostat...

    I am running a 3500 watts baseboard heater (3 heaters)
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Dec 21, 2010, 10:37 AM

    The only suggestion I have is to contact Honeywell directly to learn what the rating is of the new stat.
    mdmaynard's Avatar
    mdmaynard Posts: 40, Reputation: 1
    Junior Member
     
    #7

    Dec 21, 2010, 10:40 AM

    Thanks for the feedback.

    I hope it was just a bad connection or bad thermostat...

    I have sent honeywell an email.

    Again thanks for the feedback.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

One thermostat for two baseboard heaters wired this way [ 3 Answers ]

Hi guys, I have been upgrading my thermostats here in the house and I have a little challenge now. Two baseboard heaters that I assume are wired parallel (you will be able to confirm) had their own unit mounted thermostat. I'd like to upgrade as well but for those two I'd like to use the...

2 baseboard heaters 1 thermostat [ 9 Answers ]

I am trying to install 2 2500 watt baseboard heaters each on its own 240v 20 amp circuit. That part I can do, but I want to tie them into one thermostat, How is this done? Anyone help,Thanks

Electric Baseboard Heaters and Thermostat [ 4 Answers ]

I have 6 electric 220V heaters powered by two separate 20A circuits. All heaters are wired to a single thermostat. The thermostat is labeled 24V, and only has a small red and white wire running to it (far smaller than 10# or 12# wire.) I would like to replace this thermostat with a progammable. ...

Wiring thermostat and 2 baseboard heaters [ 1 Answers ]

Hey guys can you double check my plan for wiring my two new baseboard heaters 12/2 Romex(blk/white/bare ground) 20 amp Square D QO 240v breaker Honeywell TL8230 Line Pro 800 double pole 240v 3600w 15 amp load 2x Qmark HBB-1504 heaters 240v 6.25amps 1500w 1. Main off 2. install breaker

Electric baseboard heaters -wiring 1 thermostat to two heaters [ 2 Answers ]

I would like to heat my new garage with electric baseboard heaters. The new garage is 20X24 feet. I would like to use only one 240V #12 2 wire circuit running two heaters at a total of 3800 watts. I plan to use 2 pole 20A breakers and 2c #12 wire. I would like to have both heaters controlled...


View more questions Search