    Heat Pump Fan Delay
    We have an open loop water source heat pump, and the supply ductwork is in the trusses above the ceiling insulation. The ductwork is insulated, but not all that well, maybe an R-20. So, the fan blows cool air for a minute and a half while the TACO valve opens. Does anyone see a problem with adding a pair of relays as shown in the attached drawing so that the fan signal is delayed?
    Attached Images
     
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 13, 2010, 10:51 PM
    Many A/C outdoor units use a time delay and I believe it will do the same job but cheaper and easier. Look on Ebay for one of these then just wire it in the green thermostat circuit. http://cgi.ebay.com/New-Watsco-Adjustable-Delay-Make-Time-Delay-Relay-/320602881165?pt=LH_DefaultDomain_0&hash=item4aa56b bc8d

    You need the delay on make style and wire it into the green blower activation wire. Since it is adjustable you can play with the amount of delay till you are happy with its operation. See this also. It shows the amount of time delay available. Just follow the simple directions

    http://af1ac.ecrater.com/p/2236045/delay-on-make-timer-replacement-icm102b-for

    I have done this setup before BUT it will be up to you to make it work with your system. In the diagram you posted I do not see a timming delay device only a relay so I have no idea how you would make the setup you posted work as a delay.

    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Nov 13, 2010, 10:53 PM
    I am also under the assumption that your thermostat is using a 24 volt circuit if it is 120 volt powered just follow the package directions to solve that problem.
    Tlims's Avatar
    Tlims Posts: 4, Reputation: 1
    New Member
     
    #4

    Nov 14, 2010, 07:02 AM
    Comment on hvac1000's post
    Calling it a "fan delay" is a misnomer. I should have called it a "valve delay eliminator" because it lets the fan signal through only after the valve is open and it is dependent on the Y signal.
    Tlims's Avatar
    Tlims Posts: 4, Reputation: 1
    New Member
     
    #5

    Nov 14, 2010, 07:08 AM
    Comment on hvac1000's post
    Yes, it is a conventional 24 VAC system. Might not my circuit be safer than a time delay because it is dependent on the Y signal, not separate from it? With a time delay relay, you could have the compressor on with no fan if it were adjusted wrong.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heat won't shut off on heat pump and outside fan not running [ 2 Answers ]

My heat pump runs continually inside in heat mode but the fan motor outside won't run. If I make it cooler in the house (65 or so) it will run properly. If the a/c is on and I lower it to 70 inside the outside motor won't work again but the compressor unit runs. Have already replaced fan motor...

Heat pump fan has been running for an hour, the heat is not on or ac is this normal? [ 3 Answers ]

My electrical heat pump fan has been running for an hour or two the heat is not on or the ac is this normal?

Goodman cpl t30-1a heat pump, heat not working/no compressor or fan operation [ 5 Answers ]

The thermostat is operating/clicks on when desired temperature is more that the actual, but no action at the compressor or fan. We even switch thermostats from other unit in house and both operate the other unit correctly.

Heat Pump Fan not pushing out Air/Heat [ 0 Answers ]

We have a heat pump system. The unit upstairs runs and works fine, however the unit downstairs will kick on but won't blow any air out. The outside fan units both work properly, we just can't seem to get any air or heat to push out from the downstairs unit, what could be the problem and is it an...

20 yr old Lennox heat pump fan blows constantly in heat mode [ 5 Answers ]

20 year old Lennox heat pump - outside temps been 30's at night, 40's daytime UPDATE: I went outside and the unit is covered in frost on 3 sides! I've been reading on Google about frosted heat pump units and can't determine how to manually defrost it. Apparently, the auto defrost is not...


View more questions Search