    Breaker sizing
    I have a 66 unit panel, each need 114KVA. My question is, can I use a same breaker for all unit, or I should use a separate breakers for each unit or for for some of them?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 21, 2010, 04:42 AM
    Need to know more detail about what you have and what your trying to accomplish.

    Unit = ?
    dabbagui's Avatar
    dabbagui Posts: 3, Reputation: 1
    New Member
     
    #3

    Oct 21, 2010, 08:12 AM

    I have actually 66 units panel. Each panel should used for 4 segments and each segment have 30 motors.
    So, each unit panel should have enough power for 120 motors.
    The load for each motors is (0.5 hp, 480v).
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Oct 21, 2010, 12:36 PM
    I have no idea what your talking about.

    Units? I asked you don't explain.

    "Each unit panel... power for 120 volt motors"

    Then, "load for each motors is (0.5 hp, 480v)"

    ??
    dabbagui's Avatar
    dabbagui Posts: 3, Reputation: 1
    New Member
     
    #5

    Oct 21, 2010, 02:00 PM

    units = panelboard

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire sizing and conduit sizing [ 8 Answers ]

I am looking for confirmation on some of the info I have found and answers to a few missing pieces. This is regarding wire size and conduit size for service conductors from the meter to the breaker panel (about 30 ft away). Wire Size: 125A service needs #2 copper or 1/0 aluminum -- #6 copper...

Issues when replacing single circuit breaker with duplex breaker [ 3 Answers ]

I have a Westinghouse B20 2040CT Circuit Breaker Panel with a 200 amp main. I am remodeling my kitchen and would like to correct some of the current wiring problems I inherited when I purchased the house. A number of circuits are current heavily loaded and I want to take this opportunity to...

Can we convert the 220v breaker in to 24v breaker(vaccum ckt bkr).how [ 1 Answers ]

Can we convert the 220v vacuum ckt bkr in to 24v vcb? How. Can u explain. Can we use differential relay bkrs in the place of 24v bkr?

Electrical nfpa 70 sizing of ac equipment wire and breaker size [ 2 Answers ]

Ac equipment. Minimum circuit ampacity is 18 amps max is 40. What size wire and what size breaker?


View more questions Search