    Sup-panel feeder amperage
    Good day,

    When planning a feeder and load for a sub-panel, should the panelboard be considered a multi-outlet device and therefore you would limit the load to 80% of the breaker used in the main service panel breaker.

    For example: MSP Breaker = 100 Amps. Sub-panel load not more than 80 amps?

    If not, why not? I'm trying to prove a point to a relative.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Sep 23, 2010, 09:37 AM
    A panelboard is a mulit-outlet device?

    Here is a good place to discuss Main Panels and Sub Panels.

    There are no such things.

    Better to think of a "Main" Panel is a panelboard that happens to have the Main Service Disconnecting Means in it.

    A "Sub" Panel happens to be a panelboard that does not have the Main Service Disconnecting Means in it.

    My point is, they are both to be treated the same.

    80% derating factor is only for loads to be determined as continuous, or runs 3 hours or more, plus 100 % of loads that are not continuous.

    I know, I know, it gets confusing.

    Of course, one, I am older the older school, and derated everything 80 %, plus all I do is commercial and industrial, and it all is derated 80%.

    I digress. Back to panels, it don't matter if it is a main or a sub, rated them the same.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Updating service panel to 200 amp with feeder to 100 amp panel in old house [ 8 Answers ]

I currently in the process of converting 1000 sq ft of attached garage into living space while doing this we are updating electrical service to 200 amp new service, there is 100 amp service in the old part of the house which will remain but need to be sub paneled from the new 200 amp service. I...

Feeder size for 200a sub panel [ 1 Answers ]

What I have is an added 2 car garage with a game room added and connected to the main house. Problem is the main service had to be moved to the exterior of the new garage. I picked up this job after someone else bailed on it. Anyway its been decided to put all the existing circuits into a 200a sub...

Entrance Panel Amperage Rating [ 1 Answers ]

I just bought an older condo. The service panel in the unit does not contain the main breaker. It is located in a meter room outside. The main breaker there appears to be 125 amps (I'm assuming 220). I would like to install a combo gas/electric oven stove. There is no 220 big amperage service...

Feeder Wire for Sub-Panel [ 2 Answers ]

Hello my name is Mark and I have just purchased my first home. I was hoping someone could help me out in determining what size feeder cable I would need to run from my main panel to a detached garage. The length of the run would be 70 feet. The main panel is a 100 amp panel. I would be running 6...

Feeder line from main panel [ 5 Answers ]

I want to run a feeder line from one building to another in a 2 in. underground conduit.about 100 ft. run what size alum. Wire will I need for 125 amp sub panel


View more questions Search