    Feeder size for 200a sub panel
    What I have is an added 2 car garage with a game room added and connected to the main house. Problem is the main service had to be moved to the exterior of the new garage. I picked up this job after someone else bailed on it. Anyway its been decided to put all the existing circuits into a 200a sub about 50ft from the main service. Also the main has been upped to a 400a panel with a 300a main breaker. That's what the inspector came up with due to previous load calc on the old service.

    Question: does this sound reasonable and if so what size feeder should I use? What size breaker do I use at the main? This is a 2200 sq ft home and a 1200 sq ft addition. All new homeruns will come from the new main. Inspector also said to put a 200a main lug breaker on the sub. Help.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 11, 2009, 02:30 AM
    If I follow this correctly, the calcs show that he existing circuits need a 200 amp panel, with a 200 amp breaker at the meter/main, leaving 100 amps capacity for the new addition.

    The 200 amp sub can use #4/0 aluminum, 4 wire SER cable, as a feeder.

    Next you need branch circuit capacity at the meter/main for the remaining 100 amps to be used for the new addition.

    Did I interpret this correctly?

    Are you an electrician?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Updating service panel to 200 amp with feeder to 100 amp panel in old house [ 8 Answers ]

I currently in the process of converting 1000 sq ft of attached garage into living space while doing this we are updating electrical service to 200 amp new service, there is 100 amp service in the old part of the house which will remain but need to be sub paneled from the new 200 amp service. I...

Wiring into a new main panel (200A) and sub-paneling our existing 100A [ 8 Answers ]

I have been told that it is possible to install a new 200A main panel near our old 100A main panel, install a new weather head and when I have the power company switch the power to the new panel, then setup the old panel as a sub panel of the new. One of my main concerns is that the old panel...

Feeder Line Size [ 1 Answers ]

I am rewiring an out building and am concerned about the size of the overhead feeder wire. I have aluminum triplex feeder wire with 7 strands of wire for each line. Is this wire heavy enough to carry 200 amp service?

Feeder size [ 1 Answers ]

Hi, We are building a small art studio in our backyard. The power requirements for the building are: 1 dedicated 110V 20 amp circuit for a small kiln 1 dedicated 220V 20 amp circuit for a larger kiln 1 dedicated 110V 15 amp circuit for small wall-mounted heater/ac unit 1 dedicated 110V 15...

Feeder Wire for Sub-Panel [ 2 Answers ]

Hello my name is Mark and I have just purchased my first home. I was hoping someone could help me out in determining what size feeder cable I would need to run from my main panel to a detached garage. The length of the run would be 70 feet. The main panel is a 100 amp panel. I would be running 6...


View more questions Search