Ask Experts Questions for FREE Help !
Ask
    lancebassett's Avatar
    lancebassett Posts: 17, Reputation: 1
    New Member
     
    #1

    Jul 8, 2010, 04:53 PM
    Having the same problem 3 amp fuse keeps blowing out
    my question is I have 27.8 volts coming into the fuse holder should I have a fuse that is 3 amp with a 30 volt capacity and or can I increase the fuse
    smoothy's Avatar
    smoothy Posts: 25,490, Reputation: 2853
    Uber Member
     
    #2

    Jul 8, 2010, 05:11 PM

    What should the device be fused at?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #3

    Jul 8, 2010, 05:41 PM

    Does it blow with the t-stat off? Or just with cooing on?
    lancebassett's Avatar
    lancebassett Posts: 17, Reputation: 1
    New Member
     
    #4

    Jul 8, 2010, 05:45 PM
    Comment on Joshdta's post
    It blows while the stat is on also the fuse that I found in the stat was a 3A 250Vdoes that matter?
    lancebassett's Avatar
    lancebassett Posts: 17, Reputation: 1
    New Member
     
    #5

    Jul 8, 2010, 05:49 PM
    Comment on smoothy's post
    I don't have the mannual but from what I hear the fuse should be 3 amps does the 27.8 currentto the fuse holder have anything to do with it blowing I thought the transformer was to make the 120v reduced down to 24v ? Is it normal to see the extra 3.8v
    smoothy's Avatar
    smoothy Posts: 25,490, Reputation: 2853
    Uber Member
     
    #6

    Jul 9, 2010, 09:00 AM

    So you understand, I asked because if its actually spec'd for a 3 amp fuse. (Sometimes a wrong fuse gets installed). Then there is a malfuction that causing excessive current drain. Going too high in value can result in as a worst case situation a fire... or at best irreperable damage to the device and/or wiring.
    lancebassett's Avatar
    lancebassett Posts: 17, Reputation: 1
    New Member
     
    #7

    Jul 9, 2010, 08:12 PM
    Comment on smoothy's post
    smoothy,josh, I really appreciate your input! I went to the condo today bought more fuses and this is what I found out I turned the power off, I put the new fuse in, put the unit switch in the off position ,because there is a off switch between the
    lancebassett's Avatar
    lancebassett Posts: 17, Reputation: 1
    New Member
     
    #8

    Jul 9, 2010, 09:46 PM
    Comment on Joshdta's post
    just when I put it in the cool position, heat and fan work in on or auto position.josh thanks I really value and appreciate your opinion!! As well as your help.thanks
    JimmyTheAirGuy's Avatar
    JimmyTheAirGuy Posts: 15, Reputation: 0
    New Member
     
    #9

    Jul 10, 2010, 12:35 AM
    lancebassett,
    Control fuses can be tricky some times because the problems are usually intermediate.
    However, if you have 27.8 volts for a secondary voltage you have to many volts.
    Your secondary voltage should not exceed 24 volts. You could have a defective transformer. But, more likely the problem is going to be a short or shrunt in the coil of the compressor contactor some where in your control circuit.
    Hope this helps
    Jimmy The Air Guy
    lancebassett's Avatar
    lancebassett Posts: 17, Reputation: 1
    New Member
     
    #10

    Jul 10, 2010, 12:49 AM
    Comment on JimmyTheAirGuy's post
    Hey jimmy I just found your response if you read my last question you already know I'm not familiar with air conditions any ideas how I can test for that and if it is not that do you recommend that I replace the trans or the thermostat wadathink I app
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #11

    Jul 10, 2010, 05:59 AM

    Could be blower or compressor relay coil, or control wiring between the 2 units, or the thermostat wiring.
    Transformer or thermostat may not be your problem. Many transformers read High with no load.
    See if you can follow the control wiring ran with freon lines.
    Personally I run control wiring in conduit with the Supply lines to avouid damage.
    lancebassett's Avatar
    lancebassett Posts: 17, Reputation: 1
    New Member
     
    #12

    Jul 10, 2010, 02:29 PM
    Comment on Stratmando's post
    Hey start could you walk me through that test I have a pancake unit in the ceiling I pulled the covers there was a relay ,trans, fuseble link,two squirl fans what do I look for
    JimmyTheAirGuy's Avatar
    JimmyTheAirGuy Posts: 15, Reputation: 0
    New Member
     
    #13

    Jul 10, 2010, 07:53 PM
    I don't recommend up sizing your fuse because you obviously have a short in your control circuit. You can diagnose your system and locate the short by isolating the circuits.
    For Example:
    * Take the wires off the contactor coil replace fuse and power up.
    * Disconnect R and C from the thermostat replace fuse and power up.
    * Locate and disconnect the coil wires on your blower relay replace fuse and power up.

    You should be able to at least determine where your short is at.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #14

    Jul 10, 2010, 08:19 PM

    If it only blows when the ac is on. Most likely the contactor outside has went bad. http://www.chinacontactor.net/Produc...-Contactor.jpg
    lancebassett's Avatar
    lancebassett Posts: 17, Reputation: 1
    New Member
     
    #15

    Jul 10, 2010, 08:25 PM
    Comment on Joshdta's post
    Hey Josh, How can check if the contactor is bad ?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #16

    Jul 10, 2010, 08:30 PM

    Go to the outdoor unit, find the small t-stat wire. Take the 2 screws out of the door where the electric goes in. The t-stat wire will have 2 wire bugs on them. Just take the wires apart make sure they are not touching any metal. Put a new fuse in and give it a try. If the fuse blows, not the contactor, if it does not then the contactor is bad.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #17

    Jul 10, 2010, 09:19 PM

    I believe he is saying, if fuse blows with contactor disconnected, contactor is not your short.
    You could disconnect wires in air handler that go to contactor coil to see if the wires are shorted on the way outside.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #18

    Jul 10, 2010, 09:32 PM

    This thread is getting out of hand. See this one for some ideas:

    https://www.askmehelpdesk.com/heatin...ds-377952.html
    lancebassett's Avatar
    lancebassett Posts: 17, Reputation: 1
    New Member
     
    #19

    Jul 10, 2010, 09:55 PM
    Comment on KISS's post
    Kiss, I have a 240v step down to 24v 40amp rating transformer, I checked the power coming out of the transformer it is 27.8v the same going to the fuse holder, would you say it's the transformer or is it normal to have a trans exceed its limit of 24v
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #20

    Jul 10, 2010, 11:52 PM

    The transformer has no regulation. Only a ferroresonant transformer does and the one inside your HVAC unit isn't one.

    Here is a difinative answer: Application Notes AN-7 24VAC Transformer Output

    That basically says, it's within normal operating range of the transformer.

    I'd be curious what the input voltage is. It should divide by 10.

    Do the light bulb trick and have someone watch while you wiggle wires. Use intercom mode on a cordless phone. Use a cell phone.

    If it's not intermittant, it should be easy to find.

    The more troublesome connection is the one to the outside unit. If you disconnect wires going there at the furnace, and the light doesn't light, the problem is likely between the furnace and the outdoor unit.

    One HVAC guy I knew went as far as replacing a water to air HP in the ceiling and it still wouldn't work. Using about 10 min of my time, the thermostat wire had a short. No insulators in the metal studs and the wire was yanked during a remodel. Yep, he could have save some serious bucks.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

3 amp fuse keep blowing when airconditioning is turned on. Any suggestions why? [ 25 Answers ]

3 amp fuse keep blowing when airconditioning is turned on. Any suggestions why? Control board look fine. How do you exactly determine of there is really low voltage wires are shortened? Based on the blog, I suspect that but I have to check tomorrow. Is there a procedure of testing it starting...

Carrier blowing 3 amp fuse [ 11 Answers ]

I HAVE AN OLD CARRIER WEATHERMAKER 58SX. It keeps blowing the 3 amp fuse inside the unit on the control module. It will fire up the inducer motor, light the pilot, but when it comes time to start the blower motor, it blows the fuse and the blower motor continues to run, the inducer motor stops...

BRYANT Furnace blowing 3-amp fuse on control board [ 1 Answers ]

I have a Bryant M/N 383KAV036070AGJA, S/N 3097A08913, Series G furnace with central air that is blowing the 3-amp fuse on the control board. The furnace has been serviced numerous times over the past two years for various problems by multiple service companies. The control board was even replaced...

Carrier keeps blowing 5 amp fuse in heat setting [ 2 Answers ]

Crappier... er... Carrier Unit has blown 2 fuses in two days on heat setting. Fuse is in main blower housing. Is this a short? Any ideas? Thanks, Frustrated and Freezing...

Keeps blowing 3 Amp Fuse on Control Panel. [ 1 Answers ]

I Have A Carrier (58gsc)upflow Furnace & A/c Unit, Which Is 18 Years Old. When I Tried To Turn The Heater On , Only Blower Came On & Would Not Turn Off Unless Disconnected From Electricity. Replaced Sofar Control Unit, Thermostat,transformer Was Blown,& Finally The Limit Switch. When I...


View more questions Search