  • Jul 8, 2010, 04:53 PM
    lancebassett
    Having the same problem 3 amp fuse keeps blowing out
    my question is I have 27.8 volts coming into the fuse holder should I have a fuse that is 3 amp with a 30 volt capacity and or can I increase the fuse
  • Jul 8, 2010, 05:11 PM
    smoothy

    What should the device be fused at?
  • Jul 8, 2010, 05:41 PM
    Joshdta

    Does it blow with the t-stat off? Or just with cooing on?
  • Jul 8, 2010, 05:45 PM
    lancebassett
    Comment on Joshdta's post
    It blows while the stat is on also the fuse that I found in the stat was a 3A 250Vdoes that matter?
  • Jul 8, 2010, 05:49 PM
    lancebassett
    Comment on smoothy's post
    I don't have the mannual but from what I hear the fuse should be 3 amps does the 27.8 currentto the fuse holder have anything to do with it blowing I thought the transformer was to make the 120v reduced down to 24v ? Is it normal to see the extra 3.8v
  • Jul 9, 2010, 09:00 AM
    smoothy

    So you understand, I asked because if its actually spec'd for a 3 amp fuse. (Sometimes a wrong fuse gets installed). Then there is a malfuction that causing excessive current drain. Going too high in value can result in as a worst case situation a fire... or at best irreperable damage to the device and/or wiring.
  • Jul 9, 2010, 08:12 PM
    lancebassett
    Comment on smoothy's post
    smoothy,josh, I really appreciate your input! I went to the condo today bought more fuses and this is what I found out I turned the power off, I put the new fuse in, put the unit switch in the off position ,because there is a off switch between the
  • Jul 9, 2010, 09:46 PM
    lancebassett
    Comment on Joshdta's post
    just when I put it in the cool position, heat and fan work in on or auto position.josh thanks I really value and appreciate your opinion!! As well as your help.thanks
  • Jul 10, 2010, 12:35 AM
    JimmyTheAirGuy
    lancebassett,
    Control fuses can be tricky some times because the problems are usually intermediate.
    However, if you have 27.8 volts for a secondary voltage you have to many volts.
    Your secondary voltage should not exceed 24 volts. You could have a defective transformer. But, more likely the problem is going to be a short or shrunt in the coil of the compressor contactor some where in your control circuit.
    Hope this helps
    Jimmy The Air Guy
  • Jul 10, 2010, 12:49 AM
    lancebassett
    Comment on JimmyTheAirGuy's post
    Hey jimmy I just found your response if you read my last question you already know I'm not familiar with air conditions any ideas how I can test for that and if it is not that do you recommend that I replace the trans or the thermostat wadathink I app
  • Jul 10, 2010, 05:59 AM
    Stratmando

    Could be blower or compressor relay coil, or control wiring between the 2 units, or the thermostat wiring.
    Transformer or thermostat may not be your problem. Many transformers read High with no load.
    See if you can follow the control wiring ran with freon lines.
    Personally I run control wiring in conduit with the Supply lines to avouid damage.
  • Jul 10, 2010, 02:29 PM
    lancebassett
    Comment on Stratmando's post
    Hey start could you walk me through that test I have a pancake unit in the ceiling I pulled the covers there was a relay ,trans, fuseble link,two squirl fans what do I look for
  • Jul 10, 2010, 07:53 PM
    JimmyTheAirGuy
    I don't recommend up sizing your fuse because you obviously have a short in your control circuit. You can diagnose your system and locate the short by isolating the circuits.
    For Example:
    * Take the wires off the contactor coil replace fuse and power up.
    * Disconnect R and C from the thermostat replace fuse and power up.
    * Locate and disconnect the coil wires on your blower relay replace fuse and power up.

    You should be able to at least determine where your short is at.
  • Jul 10, 2010, 08:19 PM
    Joshdta

    If it only blows when the ac is on. Most likely the contactor outside has went bad. http://www.chinacontactor.net/Produc...-Contactor.jpg
  • Jul 10, 2010, 08:25 PM
    lancebassett
    Comment on Joshdta's post
    Hey Josh, How can check if the contactor is bad ?
  • Jul 10, 2010, 08:30 PM
    Joshdta

    Go to the outdoor unit, find the small t-stat wire. Take the 2 screws out of the door where the electric goes in. The t-stat wire will have 2 wire bugs on them. Just take the wires apart make sure they are not touching any metal. Put a new fuse in and give it a try. If the fuse blows, not the contactor, if it does not then the contactor is bad.
  • Jul 10, 2010, 09:19 PM
    Stratmando

    I believe he is saying, if fuse blows with contactor disconnected, contactor is not your short.
    You could disconnect wires in air handler that go to contactor coil to see if the wires are shorted on the way outside.
  • Jul 10, 2010, 09:32 PM
    KISS

    This thread is getting out of hand. See this one for some ideas:

    https://www.askmehelpdesk.com/heatin...ds-377952.html
  • Jul 10, 2010, 09:55 PM
    lancebassett
    Comment on KISS's post
    Kiss, I have a 240v step down to 24v 40amp rating transformer, I checked the power coming out of the transformer it is 27.8v the same going to the fuse holder, would you say it's the transformer or is it normal to have a trans exceed its limit of 24v
  • Jul 10, 2010, 11:52 PM
    KISS

    The transformer has no regulation. Only a ferroresonant transformer does and the one inside your HVAC unit isn't one.

    Here is a difinative answer: Application Notes AN-7 24VAC Transformer Output

    That basically says, it's within normal operating range of the transformer.

    I'd be curious what the input voltage is. It should divide by 10.

    Do the light bulb trick and have someone watch while you wiggle wires. Use intercom mode on a cordless phone. Use a cell phone.

    If it's not intermittant, it should be easy to find.

    The more troublesome connection is the one to the outside unit. If you disconnect wires going there at the furnace, and the light doesn't light, the problem is likely between the furnace and the outdoor unit.

    One HVAC guy I knew went as far as replacing a water to air HP in the ceiling and it still wouldn't work. Using about 10 min of my time, the thermostat wire had a short. No insulators in the metal studs and the wire was yanked during a remodel. Yep, he could have save some serious bucks.