3 amp fuse keep blowing when airconditioning is turned on. Any suggestions why?
3 amp fuse keep blowing when airconditioning is turned on. Any suggestions why?
Control board look fine. How do you exactly determine of there is really low voltage wires are shortened? Based on the blog, I suspect that but I have to check tomorrow.
Is there a procedure of testing it starting from outside unit or thermostat?
Please advise.
Appreciate the response.
Wazimi
|
|
 |
New Member
|
|
May 4, 2010, 09:49 PM
|
|
Following the question, house is built in 2005 and I don't suspect any corrosion or chewed wires.
|
|
 |
New Member
|
|
May 5, 2010, 06:35 AM
|
|
Thank you, will check it.
|
|
 |
New Member
|
|
May 5, 2010, 06:56 AM
|
|
Just quick for the test of the outside conductor, if I remove low vol- wires and set tstat on heat (gas furnace) and start the unit for control panel and new fuse test, will that make sense? Because it is not a heat-pump.
|
|
 |
New Member
|
|
May 5, 2010, 01:50 PM
|
|
I checked the contactor, it looks fine and nothing seems that has burnt. Any other suggestion?
|
|
 |
Plumbing Expert
|
|
May 5, 2010, 03:34 PM
|
|
Even though the contactor doenst appear burnt, it most likely is still the culprit. Disconnect the two low voltage wires from the contactor and turn the system to cool, if fuse doesn't blow, you need a new contactor.
|
|
 |
New Member
|
|
May 6, 2010, 12:28 PM
|
|
Thanks a lot for the responses. But my issue is still the same. I replaced the contactor with new one. Did not resolve the problem.
Still blown out fuse immediately. I disconnected the new contactor from the low voltage blue and brown wires, fired up the unit, no response to the unit to start, thent disconnected the face of the t-stat, put it back on off position, switch to cool, unit started and motor did run and blow air, but lasted only 3 minutes and fuse blew again.
Any suggestions from here?
Is my t-stat maybe defective?
Last year I replaced twice the fuse (last summer and then in winter, but lasted till now... now it keeps blowing).
What is the wiring test if I bypass the t-stat? To test if the problem is with t-stat? In that case should I disconnect the contactor from low voltage wires too?
Can it be the C-board at all?
Thanks for all your responses/
|
|
 |
New Member
|
|
May 7, 2010, 07:52 AM
|
|
Good folks, I still awaiting any suggestions.
Thank you for your time.
|
|
 |
Uber Member
|
|
May 7, 2010, 12:25 PM
|
|
Replacing the contactor was throwing money away.
Somewhere on this site, I put in the procedure for doing troubleshooting. You basically replace the fuse with two 12 V lamps that draws 30-40 VA at 12V. e.g.. About 30/12 Amps. I forget off the top of my head what bulb is a good suggestion.
Thus, you look for the bulb to light which indicates a short.
First part of the troubleshooting procedure to determine if it's G or Y.
See if the fuse blows when in fan mode (No heat or AC). This would mean a problem with "G".
Next eliminate a wiring issue. Disconnect C and Y heading to the outdoor unit at the FURNACE.
If the fuse doesn't blow then it's wiring or thermostat.
Put things back.
With the thermostat set to off and fan set to off connect R to G and to Y at the furnace
If fuse blows, then wiring is defective. If not, then stat is defective.
A multimeter would be necessary for anything else you need to do.
|
|
 |
Ultra Member
|
|
May 7, 2010, 06:02 PM
|
|
Take the stat off, red to yellow for cool
Red to white for heat
Red to green for fan
Try all of those and see when the fuse blows.
You did not by chance hit the wire outside with the weed eater while trimming, this happens a lot.
|
|
 |
New Member
|
|
May 7, 2010, 09:12 PM
|
|
Thanks a lot, will try.
You mean disconnect them, correct? And try them one by one at a time? Is this in a position while the face of the tstat off the wall?
I did check the low-vol lines, no weed eater damage...
Thanks for your help and responses.
|
|
 |
Uber Member
|
|
May 7, 2010, 09:21 PM
|
|
I tried to say the same thing, but "safer". One problem that occurs if you do this powered with R and Y is you can pop fuses or breakers for the outside unit because of the built-in delay in the thermostat.
Anywho: for cool the stat controls the indoor fan and for heat the furnace controls the indoor fan.
R to G - makes the indoor fan run.
R to Y - Makes only the outdoor compressor to run
In order to get cool, you must connect R to Y and G. You may test independently.
R to W - Makes the heater and the indoor fan run. The indoor fan will usually have a start-up delay and will not turn off immediately.
Check my other post.
|
|
 |
New Member
|
|
May 10, 2010, 12:36 PM
|
|
Problem still remains. Put a new tstat and fired heat. It runs great. As soon as tstat goes to AC, fuse blows. Checked all low voltage wiring in and out... all fine and no sign of chewed or damage.
Diagnostic LED flushes at AC setting as:
24, meaning as the panel reads: Secondary Voltage Fuse is Open check for short circuit secondary voltage (24 VAC) wiring.
2 rapid flushes followed by 4 delayed flushes.
I removed the tstat face, loosen all wirings and connected R to Y & G at the same time, turned on unit, fuse blew.
Carrier unit Model #: 58STA090---1114
Serial #: 4404A40864
Any suggestions?
Thank you,
|
|
 |
Uber Member
|
|
May 10, 2010, 02:42 PM
|
|
Because this
 Originally Posted by op
I removed the tstat face, loosen all wirings and connected R to Y & G at the same time, turned on unit, fuse blew.
Happened. It's not the tstat.
It still looks like a wiring fault. Next you need to isolate, is it Y or G that's causing problems. Just like I asked you to do earlier.
Check Y & G independently.
Do you own a multimeter?
|
|
 |
Ultra Member
|
|
May 10, 2010, 02:50 PM
|
|
Take the yellow wire off y on the control board in the base meant, leave the yellow from the t-stat on the y and try it this will tell you weather the problem is in the outdoor or indoor unit
|
|
 |
New Member
|
|
May 10, 2010, 03:13 PM
|
|
Thanks appreciate it.
So, assuming the problem is Y or G, what then... I just want to be a step ahead and resolve it when I found out of the faulty wire...
|
|
 |
Ultra Member
|
|
May 10, 2010, 04:57 PM
|
|
Do you have a ohm meter?
|
|
 |
New Member
|
|
May 10, 2010, 05:24 PM
|
|
No I do not. I will be getting one. So, assuming I have one, what is the procedure?
|
|
 |
Uber Member
|
|
May 10, 2010, 05:31 PM
|
|
Basically you need to figure out if it's Y or G. Rigth now, you know it's Y or G.
Next, you need to figure out where is the faulty segment.
Is it:
Thermostat to furnace?
Or
Furnace to outside unit.
If we assume there is a problem with "Y".
If you disconnect the wires (C&Y) at the outdoor unit, then it's not the outdoor unit. If you disconnect the wires at the furnace going to the outdoor unit and the fuse blows, then it's the wiring between the thermostat and the furnace.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Carrier blowing 3 amp fuse
[ 11 Answers ]
I HAVE AN OLD CARRIER WEATHERMAKER 58SX. It keeps blowing the 3 amp fuse inside the unit on the control module. It will fire up the inducer motor, light the pilot, but when it comes time to start the blower motor, it blows the fuse and the blower motor continues to run, the inducer motor stops...
BRYANT Furnace blowing 3-amp fuse on control board
[ 1 Answers ]
I have a Bryant M/N 383KAV036070AGJA, S/N 3097A08913, Series G furnace with central air that is blowing the 3-amp fuse on the control board. The furnace has been serviced numerous times over the past two years for various problems by multiple service companies. The control board was even replaced...
Keeps blowing 3 Amp Fuse on Control Panel.
[ 1 Answers ]
I Have A Carrier (58gsc)upflow Furnace & A/c Unit, Which Is 18 Years Old.
When I Tried To Turn The Heater On , Only Blower Came On & Would Not Turn Off Unless Disconnected From Electricity.
Replaced Sofar Control Unit, Thermostat,transformer Was Blown,& Finally The Limit Switch.
When I...