    Grounding 2 main panels on 1 meter
    I'm new to this group, but have read several threads and the answers seem well thought out and reasonable. Thanks for this forum!

    I have two, 3-phase, 200A main breaker service entrance panels, each wired (3/0) to dual lugs in a 320A meter can. They are grounded (with #2 cu) as follows:

    Panel A's ground wire runs from a lug on its (bonded) neutral/ground bar to an 8' ground rod.

    Panel B's ground wire runs from a lug on its (bonded) neutral/ground bar to a lug screwed to the metal housing inside of Panel A.

    I asked a local electrician about this, and he said it was okay, but it seems to me that this has introduced multiple points of failure between Panel B and earth.

    My question - is this okay the way it is? And if not, what's the best/proper method?

    Thanks for any suggestions.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 28, 2010, 02:26 PM
    To help with possible problems with the words, any chance of getting some photos of both panels and meter?

    Or a diagram?
    curtiseggen's Avatar
    curtiseggen Posts: 5, Reputation: 1
    New Member
     
    #3

    Jun 28, 2010, 03:37 PM
    I chose my words carefully, but it is a rather difficult thing to describe. Let me see if I can upload something to clarify...
    curtiseggen's Avatar
    curtiseggen Posts: 5, Reputation: 1
    New Member
     
    #4

    Jun 28, 2010, 05:24 PM
    Okay, here is a diagram of the situation. I'm wondering if the ground connection for Panel B is okay as built. Thanks!

    curtiseggen's Avatar
    curtiseggen Posts: 5, Reputation: 1
    New Member
     
    #5

    Jun 28, 2010, 05:26 PM
    Trying again for image...
    Attached Images
     
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Jun 29, 2010, 08:20 AM
    It is not the way I would have done it, and I see a possible ground loop in how both grounds get connected at Panel A.

    The meter neutral should be grounded to earth directly, so the system neutral is grounded.

    Then at each panel the neutral is bonded to equipment ground in that panel.
    curtiseggen's Avatar
    curtiseggen Posts: 5, Reputation: 1
    New Member
     
    #7

    Jul 1, 2010, 05:20 PM
    Thanks, tk. Both panel neutral bars are bonded to ground. Panel A goes straight to ground, but Panel B is only grounded through Panel A.

    You say that's not how you'd have done it. Which is why I submitted the question, I guess, it didn't feel right to me either.

    May I ask... how would you have done it?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I run two panels from one meter? [ 4 Answers ]

I would like to add a 100 amp panel to my outbuilding. Unfortunately for me my main household panel is maxed out. Can I run two panels from my single meter and how is this accomplished?

Grounding sub panels [ 1 Answers ]

Hi I have a separate garage with a 100 amp sub panel 70 feet from the main house. This panel has a ground rod and currently there are three wires, two hots and a neutral bonded to the rod. The hots and neutral are run underground separate from the phone and cable in separate plastic conduit...

Grounding Service Panels [ 1 Answers ]

I am looking for advise in proper grounding of service panels. I have a 200 amp disconnect at the pole under my meter. From here I run into a 100 amp service panel (about 70ft from the pole) with a 100 amp breaker. I came off this box with another 100amp breaker to a second box (about another 70ft...

Grounding a Panel and Meter Box [ 4 Answers ]

I am installing 200 amp electrical service in a new residence using 2/0 SE cable. The main breakers are in the panel. Since it is a GE panel, I have added grounding bars which did not come installed in the panel. The neutrals will all go to the neutral bars and the grounds to the grounding bars....

Grounding/neutral meter box and panel [ 1 Answers ]

I'm istalling a 100 amp service in the yard w/meter for the lake equip. The pole will have 3 conductors from the power transformer to the meter box (neutral an two hots). The ground wire from the ground rod connects at the meter box at the same lugs as the neutral? Yes? Or to the meter box...


View more questions Search