    Grounding Service Panels
    I am looking for advise in proper grounding of service panels. I have a 200 amp disconnect at the pole under my meter. From here I run into a 100 amp service panel (about 70ft from the pole) with a 100 amp breaker. I came off this box with another 100amp breaker to a second box (about another 70ft away- second building), also with a service panel with a 100 amp breaker. I have the grounds and neutrals connected in both service panels. Questions are:

    1) Should the ground and neutrals be isolated in each service panel? If so, do I run to a grounding rod from the neutral or ground bus? If it's okay to have them connected, I assume it doesn't matter which bus the ground rod is connected to.

    2) If they should not be connected in each service panel, how is the proper way to ground them? Would the first box be considered a MAIN, even though I have a 200 amp service breaker at the pole? Would the second box be considered a SUB, even though it also has it's own 100 amp breaker (same as the first box)?

    Thanks in advance for any help.

    nprranch
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 2, 2008, 06:16 PM
    This can get tricky, so follow me.

    Drive at least one ground rod (check local codes, some require two) at the service pole and connect to the neutral and equipment ground bar of both disconnects. Only here will the neutrals and any grounding conductors be allowed to be connected.

    From these two service disconnects, called Service Disconnecting Means, a separate neutral and separate equipment ground wire is needed, along with the two hots, in each feeder to each building.

    At each panel, the neutral must be insulated and isolated from the panel metal box, do not install Main Bonding Jumper, (green screw or jumper wire that is separate in the carton for the panel), at either panel. This bar will be only for white neutral wires.

    Each panel must have a separate equipment ground bar, usually purchased separately, and bolted to the panel metal box using machine thread screws.

    This bar will be only for green and bare equipment ground conductors including the equipment ground from each feeder, AND a # 6 wire going to at least one ground rod, at each building. Again, check local codes with how many rods are needed at each location.

    Any metal piping in the buildings need to be "BONDED" with a min of #8 copper wire, back to the equipment ground bar in that building's panel.

    There is no MAIN or SUB panel defined by the electric code. The main is intended to be the Main Disconnect, or Service Disconnecting Means, which in your case is at the service pole.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Running two 100 amp main panels from a 200 amp service [ 27 Answers ]

Greetings! I live in a rural country area. The electric company will be installing a pole, meter, and 200amp service with disconnect at pole. (It will require 50 foot run of service cable from pole to main load center in mobile). Currently the double wide has a General Electric 100amp Main...

400 amp service, 2 200 amp panels, 320 amp meter socket [ 10 Answers ]

Hi, this is my first post here, but I have been reading a lot and have already learned a bunch. I want to thank TK already and hope you reply to this. I am in the process of designing my electrical system for my new home. I have some electrical experience, but am by no means a pro. I am...

Two eletrical service panels with new home generator [ 5 Answers ]

Hello, We had a Carrier home generator installed due to excessive power outages. In the process, the men installed an additional elec. Box and we chose the various circuits that would get power in the event of a power failure. A friend said that we should not have two "hot" boxes. In other...

Grounding a 320 amp service [ 1 Answers ]

I have a 320 amp service I have my meter mounted on a pedestal by my house with 2 disconnects on the right side. I have 2 200 amp boxes in my house in different locations. I was wondering how I would ground my disconnects outside and if I had to ground or bond my 200 amp boxes inside and how

400 amp service with 2-200 amp panels & 320 amp socket [ 6 Answers ]

Hi TK. I am running 400 amp service into my new contruction home. The electric compnay is running a single 400 amp line to the meter. I have to split it to the two panels at that point. You had told me once before that I need a 320 amp meter socket and then run 2-200 amp lines to the separate...


View more questions Search