Grounding 2 main panels on 1 meter
I'm new to this group, but have read several threads and the answers seem well thought out and reasonable. Thanks for this forum!
I have two, 3-phase, 200A main breaker service entrance panels, each wired (3/0) to dual lugs in a 320A meter can. They are grounded (with #2 cu) as follows:
Panel A's ground wire runs from a lug on its (bonded) neutral/ground bar to an 8' ground rod.
Panel B's ground wire runs from a lug on its (bonded) neutral/ground bar to a lug screwed to the metal housing inside of Panel A.
I asked a local electrician about this, and he said it was okay, but it seems to me that this has introduced multiple points of failure between Panel B and earth.
My question - is this okay the way it is? And if not, what's the best/proper method?
Thanks for any suggestions.