    What is the size of feeder wire coming from the meater to thebreaker box
    What is the difference between main lug and breaker box
    tripolino2012's Avatar
    tripolino2012 Posts: 2, Reputation: 1
    New Member
     
    #2

    Jun 21, 2010, 04:13 AM
    What is the size of feeder wire coming from the meater to thebreaker box
    What is the size of feeder wire most commonly used from the meter to the breaker box
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Jun 21, 2010, 12:47 PM

    Okay, you have two questions here.

    The cabinet for a service panel more than likely is the same.

    The difference between a MLO "Main Lug Only" and a Main Breaker Box is the primary protection for the panel board.

    A service Panel Board with a Main Breaker is exactly that. It will have a breaker equal to the incoming service. If there is a problem, the main breaker will trip and prevent damage caused by the overcurrent.

    A MLO service panel board however does not have the protection of the main breaker and therefore it needs to conform to the NEC code.

    It can be protected by no more than six breakers or a "Main Disconnecting Means"

    As to the cable size, that is totally dependent on the size of the service amperage and whether you are speaking of a sub panel or a main panel.

    For example, if you are feeding the Main Service Panel, then you would use Table 310.15 (B)(6).

    If you are feeding a sub-panel, then you need to use Table 310.16.

    You also need to select the correct cable type, based on insulation type, whether the cable will be above ground (service drop) or below ground (service lateral).

    Distance is a factor also.

    Is not a simple process. Also, you need an electrician to do a load calculation to make sure that you have the correct service amperage ordered.

    In short, I suggest you contact several licensed electricians to get bids on doing the work and in particular the calculated load vs. connected load.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Feeder size for 200a sub panel [ 1 Answers ]

What I have is an added 2 car garage with a game room added and connected to the main house. Problem is the main service had to be moved to the exterior of the new garage. I picked up this job after someone else bailed on it. Anyway its been decided to put all the existing circuits into a 200a sub...

Feeder Line Size [ 1 Answers ]

I am rewiring an out building and am concerned about the size of the overhead feeder wire. I have aluminum triplex feeder wire with 7 strands of wire for each line. Is this wire heavy enough to carry 200 amp service?

Secondary 100 Amp Feeder Wire Size [ 3 Answers ]

Hello to all. I am running a feeder wire in 2" conduit from my 100 amp breaker in my house panel to my 100 amp garage panel approximately 160' away. I am wondering if #1-#1-#2 Aluminum is sufficient with a #6 Copper ground. Thanks for the help.

Feeder size [ 1 Answers ]

Hi, We are building a small art studio in our backyard. The power requirements for the building are: 1 dedicated 110V 20 amp circuit for a small kiln 1 dedicated 220V 20 amp circuit for a larger kiln 1 dedicated 110V 15 amp circuit for small wall-mounted heater/ac unit 1 dedicated 110V 15...

Feeder Wire for Sub-Panel [ 2 Answers ]

Hello my name is Mark and I have just purchased my first home. I was hoping someone could help me out in determining what size feeder cable I would need to run from my main panel to a detached garage. The length of the run would be 70 feet. The main panel is a 100 amp panel. I would be running 6...


View more questions Search