    Feeder size
    Hi,

    We are building a small art studio in our backyard. The power requirements for the building are:
    1 dedicated 110V 20 amp circuit for a small kiln
    1 dedicated 220V 20 amp circuit for a larger kiln
    1 dedicated 110V 15 amp circuit for small wall-mounted heater/ac unit
    1 dedicated 110V 15 amp circuit for a 2 gallon water heater
    1 general purpose 110V 15 amp circuit for lights and small plug-in electrical devices like radio, etc.

    So my question is this: What size wiring does the feed to studio need? The electrician has put a 70 Amp 220V breaker in the main panel for the feed (which I agree with), but he has run only #8 AWG wire. If I'm reading code correctly, the feed should be #4 AWG, shouldn't it?

    Thanks!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 11, 2006, 03:59 PM
    The wire insulation is probably either THHN/THWN or XHHW, and I am assuming copper wire.

    The highest ampacity rating of both insulation types is 55 amps in the 90 Deg C column.

    This column can only be used if the terminals are rated 90 Deg C also. The terminals of the 70 amp breaker and the subpanel is most likely only rated at 75Deg C, and the wire is only rated at 50 amps.

    You are correct, the wire should be #4 copper THHN/THWN or XHHW.

    Did the electrician apply for a permit? And will this work be inspected?

    Either the breaker needs to be changed to a 50 amp breaker, or the wire changed to #4 copper.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Size of A Coil for AC [ 8 Answers ]

Hi Guys I want to buy an AC 2 ton but I have a fairly large air plenum on my furnace about 20 by 22 inches and any AC’s that I have looked at come with a smaller A Coil so if I used this it would greatly reduce my air flow. The A Coil looks like it is meant for a furnace in an apartment size...

Feeder Wire for Sub-Panel [ 2 Answers ]

Hello my name is Mark and I have just purchased my first home. I was hoping someone could help me out in determining what size feeder cable I would need to run from my main panel to a detached garage. The length of the run would be 70 feet. The main panel is a 100 amp panel. I would be running 6...

Feeder line from main panel [ 5 Answers ]

I want to run a feeder line from one building to another in a 2 in. underground conduit.about 100 ft. run what size alum. Wire will I need for 125 amp sub panel

Reduced Neutral for Subpanel Feeder [ 2 Answers ]

Hello, I am adding a sub-panel for a new cooktop and double wall oven. They are rated 9KW and 7.5KW. I already have 1" EMT run from my main panel to a good location under the kitchen in the basement (about 40'). I have some wire and a load center on hand that I would like to use if I can,...

Right Size? [ 5 Answers ]

Hi, Has anyone tried right size? It's some kind of weight loss smoothy or drink or something. I was wondering if anyone has tried it, how it tasted, and if it worked? Thanks...


View more questions Search