    Does code specify certain dimension for relocating a panel in KY?
    My Mom and Dad had a house fire and we had to gut the finished basement as well as part of the upstairs. In the process of repairing and replacing the wiring, I want to upgrade their service from 200 amps to 400 amps with 2-200 amp panels. One panel would be upstairs and the other one would be downstairs for the finished basement.

    I understand that I can possible use a double lug nut at the meter base to feed both panels, but do I have to have a disconnect at the meter base or are the main disconnect in the panels OK? What other options would I have to split 400 amps to 2-200 amp panels?

    What are the code guide lines for locating a 200 amp panel in living space? As planned the panel is inserted into the wall so that it will be flush with the drywall. What other things should I consider?


    Thanks
    Donnie LM
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Apr 30, 2010, 08:07 AM

    The utility dictates the requirements for the service and even may specify the bases that may be used. They specify the height of the meter, etc.

    The outside disconnect is typically required when x' of cable exists past the meter. I don't now what x is. (10' possibly)

    You may be able to feed the house with a meter base containing two 200 A breakers if the base is approved by the utility. In our area the bases have to have a sticker. All local distributers will have the approved bases and stickers for the surrounding area.

    There are some clearance issues for the panel. Again, I hope someone will come around with the numbers.

    You cannot locate a panel in a closet.

    There is a sticky on how to read the NEC online in the beginning of the "Electrical & Lighting" topic.

    Generally the bonding will be done at the first disconnect. Usually two ground rods are required.

    Copper plumbing must also be bonded too.

    Hopefully, someone will come around and fill in the particulars.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Apr 30, 2010, 10:27 AM

    Here is a thread mentioning the clearances: https://www.askmehelpdesk.com/electr...ion-97671.html
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Apr 30, 2010, 01:28 PM
    Disconnects are needed immediately as the cable from the meter enters a building, 10 feet of exposed cable inside is the max an inspector will ever allow, if that.
    When panels are in a building any distance beyond that. Disconnects are installed at the meters. There are 320 amp meter sockets for residential that have two 200 amp breakers built-in just for this type of service.

    Check with your utility for the type meter enclosures are allowed, check the manufacturers they allow, one or more of them will offer that type of meter /disconnect.

    Not just copper piping, but all metal piping needs to be bonded. If you have a metal water line, it will be your primary grounding electrode.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Relocating sub panel 120/208 4 wire. [ 4 Answers ]

Can I use a junction box to splice my feeder wires. I would like to see if code allow that. And if the code says I can not do that what are my options beside running a new set of wires. Can you please help? Thank you.

Relocating eletrical panel (Southern Calif) - costs, feasibility [ 8 Answers ]

We're looking into what it would take to relocate the eletrical panel in our home. Currently the panel is located on the outside wall adjacent to our son's bedroom wall, and we're seeing an extremely high reading of EMF all throughout his room, particularly on the wall where the panel is, but also...

Relocating my electrical panel [ 2 Answers ]

I am relocating my electrical panel to a safer place approximately 10 feed away. The original panel is 100-amp with about 13 circuits. I want to install a newer panelwith possibly more spaces for future circuits expansion. My questions are 1) with the incoming 100amp from Edison, I believe it is a...

Relocating Service Panel [ 3 Answers ]

I am changing my electrical service from overhead to underground. At the same time I am relocating it and replacing the existing rusted service panel with a new meter base, service panel (MBSP) combination. I have a couple questions: The new location is further from the home's main panel. Can I...

Upgrading/Relocating my service panel [ 1 Answers ]

I'm upgrading my service panel mainly because I need more breaker space, but will eventually need more juice. I'm an electrical engineer, but not a electrician, so I am fully aware of the principals, just not the code and best practices like electricians are, though I have been studying the code...