    Relocating Service Panel
    I am changing my electrical service from overhead to underground. At the same time I am relocating it and replacing the existing rusted service panel with a new meter base, service panel (MBSP) combination. I have a couple questions:

    The new location is further from the home's main panel. Can I connect additional SER to the existing SER? If so what types of connectors and junction box should I use? The current distance from the service panel to the main panel is about 25 feet. The new service panel will be about 60 feet from the main panel.

    I have spoken with both the power company engineer and the county inspector and I can choose to mount the new MBSP on a pole or directly to the house. The home is a two section manufactured home and it is unlikely that it will ever be moved. Is there an advantage to either mounting location?

    Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 13, 2007, 05:02 AM
    Yes, SER cable can be extended. Need to know the size of the SER cable to size the junction box and wire connectors. Also, will the box be inside or outdoors?

    Not familiar with the acronym MBSP.I assume this is the Main Breaker. 4 wire cable is required from the main to the panelboard. Whether this main is pole or building mounted will dictate how much 4 wire cable is needed. Conveinence is another factor.
    burgerbost's Avatar
    burgerbost Posts: 2, Reputation: 1
    New Member
     
    #3

    Oct 15, 2007, 05:40 AM
    Thanks... the MBSP was a shorthand for "meter base service panel" - sorry for the confusion, I added it after the first use of the words in attempt to reduce my typing.

    The SER wire is 4/0,4/0,4/0,2/0. What size junction box and connectors would you recommend? The junction box will be located in the crawlspace.

    The meter base service panel will be located beside or on the home, about 60 feet from the breaker box.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Oct 15, 2007, 06:11 AM
    The min size box would be 12" x 12". This is a minimum, and is just enough room.

    Unless your really good at forming conductors and splicing. I would use a PVC 18" x 18" x 6" deep box.

    If you use a metal box, be sure to ground the box also. Using a PVC box will be easier.

    For connectors, I would use something similar to the IT Series, found on page 1 of :
    http://www.nsipolaris.com/pdf/polaris.pdf

    These work very well, need an Allen Wrench to tighten the connector, and they are already insulated.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Installing second service panel [ 1 Answers ]

QUESTION: I am finishing off my basement and would like to add a service panel box in the basement. I have a 200amp panel box in my garage with 11 open slots out of 32. The builder pre wired a wire from the panel to the basement. The wire has a orange shield with #10 wire. There are 4 wires (3 and...

200 AMP Service panel to 200Amp Sub Panel [ 1 Answers ]

I getting new 200Amp service to surface mount service panel. I want to run 2oo cable to bring it sub panel in my Garage which is approx 120Ft Run through ceiling. 2 Questions 1. Is there any ristriction on running a 200AMP inside house to garage ? 2. I got a dirt cheap subpanel that has...

Upgrading/Relocating my service panel [ 1 Answers ]

I'm upgrading my service panel mainly because I need more breaker space, but will eventually need more juice. I'm an electrical engineer, but not a electrician, so I am fully aware of the principals, just not the code and best practices like electricians are, though I have been studying the code...

Wire at the service panel [ 1 Answers ]

I am installing a GEŽ 30" Free-Standing Electric Range(JBS55WK/CK/BK). It can use a 3 or 4-WIRE CONDUIT INSTALLATION plug from the range to the outlet. I have a double braker space available at the service panel. I have installed brakers into the panel for outlets and lights and then had them...

Service panel in bathroom OK? [ 1 Answers ]

We are going to finish our basement and our electrical service panel in the corner of a room where we would like to build a new bathroom. Can we have the service panel in a closet in the new bathroom or would that be a hazard?


View more questions Search