    Bryant Plus 90 350MAV - No heat in the morning
    First post!

    All,
    I have a Bryant Plus 90 350MAV on propane. Yesterday I woke up to a 58degree house. Night/Morning temperature is set to be 65 degrees on digital thermostat. Thermostat stated "In Recovery" on display that morning and would not control the HVAC system even when elevating temp manually. I was able to get the unit to work by shutting power off and then back on to the HVAC unit (unfortunetly I did not check for error codes). That same morning I also heard the inducer motor start, but only run for maybe ?3 seconds? And then shut down. This was not the blower motor that I heard. The unit ran perfectly all day long.
    This morning same issue, cold house and "In Recovery" stated on the thermostat. I am use to "In Recovery" for use in A/C mode, but not for Heat.
    Sorry, still no codes to report, but will certainly obtain them if it fails again. I cannot get the unit to fail as of right now.

    Diagnostics so far include:

    Verified wiring connections (all good)
    Cleaned high temp sensor (not dirty)
    Cleaned flame sense rod (not dirty)
    Verified air filter (not dirty)
    Cleaned condensation trap and lines (somewhat gunky)
    Verified pressure switch operates (by pulling and reinstalling vacuum line when unit operates properly)
    Verified inducer motor capacitor
    Inducer motor spins freely

    What could cause the inducer motor to shut off shortly (3-5 sec) after being told to turn on? Suspect board but want to know how to verify.

    I am currently shutting off the heat for the day to try and reproduce the night time situation.

    Any help would be greatly appreciated. Thank you.
    4FanTrashCan's Avatar
    4FanTrashCan Posts: 2, Reputation: 1
    New Member
     
    #2

    Mar 16, 2010, 10:25 PM

    Attempting to simulate issue by lowering the house temp to 65 through the day produced no results. The furnace kicked in as soon as the thermostat reached 64 degrees.
    All operations function properly as long as the inducer motor does not get turned off prematurely.

    Current operation when working properly:
    Thermostat requests heat
    Inducer motor starts
    Relay on board trips (few seconds later) (assume from pressure switch)
    Ignitor starts to glow
    Gas solenoid trips
    Burners light
    Blower begins to run
    House gets warm :-)
    Set temp is reached
    Blower shuts off
    Rinse and repeat!

    Any input on the culprit that would shut down the inducer motor within 3-5 sec of starting up and cause the HVAC to not respond to an automatic or manual heat request from the thermostat (Honeywell CT3650 digital/programmable)?
    I understand the "In Recovery" message to indicate that the thermostat is turning on the HVAC a little at a time in order to gradually get the house from 65 degrees to 67 degrees at the set time of 6:45 am. Amazing what reading the manual can do for you. I will shut this "Smart Response" feature off and observe for changes. Thanks in advance for any input.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #3

    Mar 17, 2010, 05:21 AM

    Does it work fine if you lock you stat to a set temp, not using the program? Also. Sounds like you may have a drain problem. At night time when the temp is still colder the drain could be stopped up causing the pressure switch to kick in and out.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bryant plus 90 350mav code 34/14 [ 5 Answers ]

I have a Bryant 350mav that is giving a code 34 followed by a code 14 . I checked the intake and exhuast pipes and they are clear. What next? It is blowing cold air, cycles the 3 times and then locks again.

Bryant 350mav igniter [ 1 Answers ]

I have a vintage Bryant 350 MAV that is temperamental. The gas will not ignite unless the igniter is in a perfect position. What is the "exact" igniter replacement part for this unit? BTW, all the items have been checked professionally, gas flow (in and out), gas pressure, air flow, air pressure,...

Repair of furnace blower for Bryant 350MAV [ 2 Answers ]

I was told by a service repair firm that the blower motor and wheel needs replacing for a Bryant Model 350MAV condensing gas furnace (10 years old). There is quite a bit of noise when it runs and the unit vibrates at bit at the blower housing. His cost was nearly $1000. I think I can do it...

Bryant 350MAV only runs in the mornings [ 6 Answers ]

Hi Everyone, I have a strange intermittent problem with my Bryant 350MAV furnace that has arisen in the last couple of months, since the weather started to cool here in Los Angeles. I usually turn off the thermostat at night when I go to bed, then manually turn on the heat in the morning when...

Bryant Model 350MAV Furnace [ 3 Answers ]

Hi, I recently had a furnace repairman in who told me our inducer on our Bryant Model 350MAV furnace needed to be replaced. He said the total cost would be $1075.00, including $890.00 for the inducer. This seemed high to me. Can anyone give me an idea of what this repair should have cost,...


View more questions Search