    Goodman gmnt080-4 ignitor
    I have a Goodman GMNT080-4 Furnace. It would not ignite, I changed the ignitor and it worked for 2 weeks. This morning it failed to ignite. Could the ignitor have gone bad again?
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Feb 14, 2010, 12:10 PM

    Remove the front panel to expose the burner area, then observe operating sequence. Does the ignitor glow? If not, check the status light on the circuit board - flashing indicates a fault. Check the code list label on the inside of the front panel. If the ignitor glows but no flame is observed, check the rollout switches that surround the burner housing. If any are "popped", a problem with the heat exchanger may exist.
    Attached Images
      
    fivemjs's Avatar
    fivemjs Posts: 4, Reputation: 1
    New Member
     
    #3

    Feb 14, 2010, 12:26 PM
    I unplugged the ignitor and connected a meter. I am getting 110v at the connector.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #4

    Feb 14, 2010, 12:54 PM
    Quote Originally Posted by fivemjs View Post
    I unplugged the ignitor and connected a meter. I am getting 110v at the connector.
    Is the ignitor element visibly damaged? Check continuity through the ignitor - should be about 90-100 ohms at room temperature. The voltage you are reading at the connector is correct, but no load is present when you are measuring it. A more accurate voltage reading would be measured if the meter probes can be inserted into the connector while the ignitor is being powered.
    Attached Images
     
    fivemjs's Avatar
    fivemjs Posts: 4, Reputation: 1
    New Member
     
    #5

    Feb 14, 2010, 03:38 PM
    Thanks, will check continuity. Is there a trick to removing/installing the ignitor.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #6

    Feb 14, 2010, 03:52 PM
    Quote Originally Posted by fivemjs View Post
    thanks, will check continuity. Is there a trick to removing/installing the ignitor.
    Treat it like an egg, & don't touch the element with your bare hands.
    fivemjs's Avatar
    fivemjs Posts: 4, Reputation: 1
    New Member
     
    #7

    Feb 14, 2010, 04:25 PM
    No continuity through ignitor. 110V going through with ignitor connected. My problem with installing the ignitor is the furnace is set up as a down flow and sits on an A/C coil. Thanks again, I'm going to get another ignitor.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #8

    Feb 14, 2010, 05:53 PM

    The failed replacement ignitor should still be in-warranty. Take it & the receipt with you for exchange.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman furnace GMNT080-4 furnace runs good for a while then has to be manually reset [ 5 Answers ]

I have a Goodman GMNT080-4 (90%). I'm having the same problem As Streatherg did back in the Nov 2006 question. I reviewed his article and tried Every thing on there but seems to be doing the same thing. The furnace kicks on for about an hour then locks out and has to be manually reset threw...

Goodman and igniter or ignitor [ 3 Answers ]

Goodman model GDT070-3B Light blinks 3 times -- the codes indicate the info below. Pressure switch failure to close -- Venter pressure switch vent blockage. The small motor starts and then I can hear gas flow (can smell a small amount later) and then it shuts down. There is never a flame. ...

Goodman furnace ignitor problems [ 7 Answers ]

Having an issuse with my goodman furnace. Ignitor turns red, flame comes on, and then goes out. Ignitor will head up again, flame on, and then off. THis repeats. I've taking off the sensor and cleaned it to a sparkly new look. Taken the burner housing out and cleaned them individually of all...

Goodman gpd075-3 ignitor [ 0 Answers ]

I have a goodman gpd-075-3. The ignitor ignites for about 4-5 seconds then kicks off. It will do this every 1-2 mintues. Why won't it stay on?

Location of goodman ignitor [ 2 Answers ]

I had a technician come out to check my furnace and told me that I need a new ignitor for a goodman furnace. He removed the ignitor and I ordered one online but I am not sure where the ignitor is located at within the furnace.


View more questions Search