    Goodman furnace ignitor problems
    Having an issuse with my goodman furnace. Ignitor turns red, flame comes on, and then goes out. Ignitor will head up again, flame on, and then off. THis repeats. I've taking off the sensor and cleaned it to a sparkly new look. Taken the burner housing out and cleaned them individually of all debris. Still the same problem.

    Is the ignitor supposed to stay glowing while the flame is burning? Is there any cleaning to the ignitor that needs to be done?

    I'm at a bit of a loss here and the temp is down in the low 20's. Getting COLD ON THE BACK END OF THE HOUSE!
    twoshy6180's Avatar
    twoshy6180 Posts: 6, Reputation: 1
    New Member
     
    #2

    Dec 10, 2009, 02:58 PM

    All these views and no ideas? :(
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #3

    Dec 10, 2009, 03:12 PM
    Check the status light - blinking indicates trouble. Observe after ignition trial failure. Locate the label with codes & instructions inside blower panel.
    Attached Images
     
    twoshy6180's Avatar
    twoshy6180 Posts: 6, Reputation: 1
    New Member
     
    #4

    Dec 10, 2009, 03:21 PM

    Knew to look there. The light indicated no issues
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Dec 10, 2009, 03:49 PM
    Just because you cleaned the flame sensor does not mean it is all good. Do the test below.
    Attached Images
  1. File Type: pdf Doc1.pdf (42.4 KB, 411 views)
  2. twoshy6180's Avatar
    twoshy6180 Posts: 6, Reputation: 1
    New Member
     
    #6

    Dec 10, 2009, 04:15 PM

    Oh jesus... I think you just asked me to test something with a gadget that I do now own :/

    Figures... was hoping NOT to call anyone in. Man oh man
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Dec 10, 2009, 04:36 PM
    To be in the HVAC trade and work on furnaces you need to spend a lot of money on test equipment. Your complaint about your furnace operation still indicates that the flame sensor is the problem. Now that could be a bad, loose or deteriorated wire that runs from the flame sensor to the control or a bad flame sensor itself. You tried cleaning it so the next step is testing.
    twoshy6180's Avatar
    twoshy6180 Posts: 6, Reputation: 1
    New Member
     
    #8

    Dec 10, 2009, 05:16 PM

    Oooooooooook... well thank you, sir. For the assistance. Greatly appreciated.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman furnace problems [ 21 Answers ]

Hi - I have a Goodman GPM furnace. It works intermittently. I replaced breaker, thermostat, Control board and surface igniter. All appears well on start up sequence ; blower runs and igniter heats up and then turns off as no gas comes out. Control board codes says OK. Can anybody recommend what to...

Goodman furnace problems [ 3 Answers ]

Son in law has a Goodman natural gas furnace. No heat. LED is flashing 4 times ('Upper limit open' is the message associated with this error). The blower motor turns on, the exhaust motor (I think that's what it is) turns on for about 10 seconds then turns off. Tried changing the air filter (was...

3 yr old Goodman Gas Forced Air Furnace problems [ 10 Answers ]

If thermostat is set to 70-90 degrees the furnace burner and blower will run constantly and the temp never gets above 68 degrees in the house. I have a Lux programmable thermostat and was thinking of replacing it with a Honeywell. I have a new filter. Any ideas? The weather has been in the...


View more questions Search