New Member
|
|
Nov 17, 2006, 09:23 AM
|
|
No power to thermostat, no fuses
I have a International Comfort Products heating and AC unit. The problem I am having is that the blower runs constantly and there is no power to the thermostat. I can find no fuses on the unit. None indicated in the schematic either. The transformer checks out OK, the wirng checks out OK also. Any suggetions would be appreciated. I am unsure if it could be a limit or pressure switch somewhere or if they could cause this type of problem.
|
|
 |
Uber Member
|
|
Nov 17, 2006, 11:23 AM
|
|
May be 2 separate problems. If you have 24 volts on the secondary of the transformer and no power at the thermostat, you may have a bad connection. Some thermostats must have a battery.
The fan running running constantly likely is a stuck relay. Before coughing up for a new circuit board, locate the high temperature limit switch and disconnect it. If the fan still runs, likely it is the relay.
|
|
 |
Ultra Member
|
|
Nov 17, 2006, 02:25 PM
|
|
Do you have 24 V at the furnace R and C terminals? If so the wire is bad between the furnace and the stat. If you are sure you have 24 V at the transformer and not at the thermostat terminals in the furnace, you need to look for a blown safety device, e.g.. Fusable link, roll-out limit, main limit etc. Be aware that if one of these safties trip there is probably a good reason, they are after all safety devices.
|
|
 |
New Member
|
|
Nov 20, 2006, 07:33 AM
|
|
I do not have any voltage across R and C. I do have 29.5 volts at the transformer. The limit swictes disconected it still runs. I can not find a fusible link. But, on that I am not sure what I am looking for. I also tapped on the relay to no avail. I do have four wires to the thermostat. R,W,Y,G. On the board I have C,G,Y,W and R. The wires are connected with G,Y,W,R to the thermostat, A wire is connected to C and Y that runs out to the condenser which is currently disabled (Main Pulled).
|
|
 |
Uber Member
|
|
Nov 20, 2006, 08:59 AM
|
|
Disconnect the wires between where you measure the 29 volts and the R & C terminals where it is dead. If one is open, carefully follow it. If it has a fat place molded into it, that would be fusible link. I would cut it out and replace it with an inline fuse rated the same as transformer output. Otherwise look for a flexible place in the wire where the conductor may be broken under the insulation.
|
|
 |
New Member
|
|
Nov 20, 2006, 09:44 AM
|
|
The transformer connects to the control board. I can find no anomalies in the wiring. I did just find out that the AUX limit and Pressure switch are not getting power. Should they be passing 24 volts?
|
|
 |
New Member
|
|
Nov 20, 2006, 10:04 AM
|
|
After further review... The pressure switch is fed by the Gas Valve. I have power to the gas valve and no power coming out.
|
|
 |
Uber Member
|
|
Nov 20, 2006, 10:09 AM
|
|
Do you mean the transformer is soldered to the board? If so, look for a fuse on the board somewhere. Otherwise, check between where the transformer connects to the board and the R & C terminals.
Usually one terminal of the switches will connect to the R terminal.
|
|
 |
New Member
|
|
Nov 20, 2006, 12:10 PM
|
|
It has wires connected and it is all pretty wide open and in good view. I even pulled the board to check behind it. No luck. How do these gas valves work? Could it be faulty?
|
|
 |
Uber Member
|
|
Nov 20, 2006, 12:36 PM
|
|
The way the gas valve works is that power flows from the transformer to the R terminal to the thermostat which switches it to the W terminal. The control board then switches power to the gas valve once it verifies other things are ready. That isn't your problem. Your problem is between the transformer and the circuit board. Is it possible you have a second transformer, and the one you are checking isn't the one that supplies power to the board?
|
|
 |
New Member
|
|
Nov 20, 2006, 01:43 PM
|
|
Thanks for the explanation. No for another transformer.
|
|
 |
New Member
|
|
Nov 20, 2006, 02:02 PM
|
|
Thanks for the info. I only have one transformer.
|
|
 |
Ultra Member
|
|
Nov 20, 2006, 03:42 PM
|
|
You need to find the open device between the +24 V from the transformer to the R terminal at the furnace. I don't see how you are getting 24 V to the gas valve if not at R or W in the furnace. You will not measure voltage coming out of the gas valve since that would be C (common)(Ground). I still need to know more about your furnace to help much. How many wires go to the gas valve, not including the green wire hooked to the body of it?
|
|
 |
New Member
|
|
Nov 21, 2006, 06:37 AM
|
|
The gas valve is a honeywell SV9501. It has a connector with four wires(to the board) and a connector with three(ignitor). The transformer at the board is OK. There is no power at the board to the blue wire that goes to the limit switches and then the gas valve.
|
|
 |
New Member
|
|
Nov 21, 2006, 06:46 AM
|
|
I reread your previous post. I assume from what you said that I should get no power to the blue wire at the board.
|
|
 |
Ultra Member
|
|
Nov 21, 2006, 03:15 PM
|
|
If you have 24 volts going to the board from the transformer, and no voltage at R you have a bd board or you are overlooking a fuse. It could be an automotive type fuse or an in-line type fuse.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
No power to thermostat
[ 19 Answers ]
Hi,
I was trying to replace my old stat with a new programmble one. I had turned off the furnace before installing new one. But the new one didn't work and so, I put the old one back on. But the old one does not power now and display on the old stat does not come up. Can any one help me here...
Need Help - Getting "No AC Power" with Hunter Thermostat
[ 2 Answers ]
Installed a new Hunter Thermostat today and I am getting "No AC Power". So I looked in the fuse box and the 5V that connects the Black and Red wire was blown. I since replaced the fuse with a new one and it also blew. Please help. It gets pretty cold at night.
No power to thermostat
[ 2 Answers ]
I recently had a pool heater installed. The electrician installed it to the incorrect voltage. We found this out when we tried to power up the pool heater. Right after he came back and installed it to the correct voltage, the thermostat and heat pump to my house quit working. It is getting no...
No power after thermostat replaced
[ 3 Answers ]
Ok... I know better... but since I was dealing with low voltage... I figured no harm... WRONG! :eek: I should have turned off the breaker when replacing my thermostat... enough said. I replaced my thermostat (simple comfort 3001) with a honeywell RTH6300b because the simple comfort display was...
No Power to Thermostat
[ 2 Answers ]
We have two electric central A/C units - one upstairs, one down. We discovered that the upstairs A/C unit was running 24/7 making the upstairs very cold (and a $680.00 electricity bill). The original Honeywell programmable thermostat was not shutting it off regardless of the room temp -vs-...
View more questions
Search
|