    No Power to Thermostat
    We have two electric central A/C units - one upstairs, one down. We discovered that the upstairs A/C unit was running 24/7 making the upstairs very cold (and a $680.00 electricity bill). The original Honeywell programmable thermostat was not shutting it off regardless of the room temp -vs- program.

    Last night, I went to Home Depot and purchased a replacement 5-1-1 Honeywell thermo. After installing the new thermo, there was no power to it.

    The old thermo was

    Blue Wire to C terminal on thermo
    Red Wire to R
    Yellow Wire to Y
    Green Wire to G
    White Wire to W

    The new thermo was wired

    Blue wire (capped & taped)
    Red Wire to R & Rc (factory supplied jumper)
    Yellow Wire to Y
    Green Wire to G
    White Wire to W

    I reinstalled the old thermo and there was no power to it either. I tried touching the red and green wires together and nothing happened, so I assume I have shorted something out.

    My local utility sent a contractor out to seal our systems, so they have taped and applied a plaster/glue looking sealant on both units in the attic. I can't determine how to open the unit to access the control panel to see if I blew the fuse.

    Before I tear everything up, is there another test/troubleshooting step I can take?

    Thanks
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Jul 24, 2005, 11:22 AM
    Usually there is a 24 volt AC transformer in the furnace with the secondary winding connected to a red wire running to the thermostat and a blue wire, common, to the gas valve, A/C relay, and fan relay. From the thermostat there will be white wire to the gas valve, yellow to the A/C, and green to the fan. The thermostat is wired to switch the power from the red to the white, yellow, and green as needed with the blue completing the circuit. Most thermostats and furnaces have the contacts labeled R, B or C, W, Y, and G for the corresponding wire colors. It may be wired to have the A/C control wires return to the furnace and its controls and then a second wire goes to the A/C unit. Internal wiring may replace the green wire if the thermostat does not give you the option of fan only or continuous fan. Digital or programmable thermostats may need the blue wire connected to them.

    If you do not have 24 volts between the red and blue wire at the thermostat, you have no choice but to follow them back to wherever the transformer is and checking it. Shorting the red to the green should have started the blower. If the thermostat is A/C only, it is possible the green and white wires are not connected. Shorting red to yellow, should start the A/C. It must have 120 volts in and 24 volts out to the red and blue wires.
    dboeth's Avatar
    dboeth Posts: 2, Reputation: 1
    New Member
     
    #3

    Jul 29, 2005, 12:55 PM
    Problem Solved
    The cause of the problem was a blown fuse on the circuit board located in the furnace unit in our attic. Apparently when the new thermostat was hooked up, the blue wire that was attached to the "C" terminal on the original Honeywell thermostat should have been capped and insulated rather than connected to the "B" terminal on the new thermostat.

    The Honeywell quick start guide for the new thermo had the incorrect wiring instructions, but the actual user manual clearly said not to connect the fifth wire.

    Lesson learned----read all of the materials before starting the job.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

No power to thermostat [ 19 Answers ]

Hi, I was trying to replace my old stat with a new programmble one. I had turned off the furnace before installing new one. But the new one didn't work and so, I put the old one back on. But the old one does not power now and display on the old stat does not come up. Can any one help me here...

No power to thermostat [ 2 Answers ]

I recently had a pool heater installed. The electrician installed it to the incorrect voltage. We found this out when we tried to power up the pool heater. Right after he came back and installed it to the correct voltage, the thermostat and heat pump to my house quit working. It is getting no...

Power dvd 5 [ 6 Answers ]

Right, I need some help with an error I keep getting while trying 2 watch dvds. It says that my " tv out put port of my diplsay card is not working properly" and I don't know how to solve this problem.. can anyone help?

No power after thermostat replaced [ 3 Answers ]

Ok... I know better... but since I was dealing with low voltage... I figured no harm... WRONG! :eek: I should have turned off the breaker when replacing my thermostat... enough said. I replaced my thermostat (simple comfort 3001) with a honeywell RTH6300b because the simple comfort display was...


View more questions Search