Ask Experts Questions for FREE Help !
Ask
    dugstone13's Avatar
    dugstone13 Posts: 3, Reputation: 1
    New Member
     
    #1

    Dec 5, 2009, 08:30 PM
    Bryant 90 plus 398A, only lights and heats when the burner compartment is open
    The draft inducer starts, but pilot burner only clicks and lights when burner compartment cover is off.
    dugstone13's Avatar
    dugstone13 Posts: 3, Reputation: 1
    New Member
     
    #2

    Dec 5, 2009, 08:42 PM

    It is a natural gas furnace. It has a 3 wire pilot burner. When the thermostat calls for the furnace to turn on, the draft inducer motor starts running, but the pilot burner is not even trying to light, no clicks no sparks, nothing. If I take off the cover of the burner compartment, the furnace fires right up and runs like there is nothing wrong.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Dec 5, 2009, 09:00 PM

    Check for air restrictions in the combustion air.

    Probably the pressure switch: http://www.xpedio.carrier.com/idc/gr...e=PdfHighlight

    Schematic is here:
    http://www.xpedio.carrier.com/idc/gr...e=PdfHighlight

    Switch 7P.

    The schematic isn't helpful.

    First attach a voltmeter between the C and NC contacts and operate with the door open. There should be a change of state. I suspect it's 24 VAC although it's impossible to tell.

    Then run wires out a hole to the meter and put the cover on.
    Check for the same change of state.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #4

    Dec 6, 2009, 06:48 AM

    With the burner enclosure open, look up through the strainer in the air vent coupling. If debris is visible, remove pipe and clean out. Also check outside vent terminations for blockage.
    dugstone13's Avatar
    dugstone13 Posts: 3, Reputation: 1
    New Member
     
    #5

    Dec 7, 2009, 04:55 PM

    Thanks, I tore it apart cleaned it good, but didn't find any obstructions, I tapped(beat on) on the pressure switch and it has been working for a couple of days now, I got a new pressure switch for when it does happen again, I will be ready with a replacement.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Dec 7, 2009, 05:06 PM
    Might as well replace the switch now since it will break again when its 20 below zero and you just got home from work if you know what I mean.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

6yr old Bryant furnace burner continually on-off-on-off [ 7 Answers ]

After the furnace heats to the desired setting of the thermostat the gas flow to the burner stops and starts every few seconds with the igniter also starting and stopping. Igniter is 2yrs. Old and won't last long operating like this.

Bryant furnace burner cutting out [ 1 Answers ]

I have a 10 year old Bryant model 376CAV (92,000 btu) downflow furnace. The electronic igniter will glow at the appropriate time and ignite the flame but the flame will cut out shortly after the ignitor shuts off. This happens repeatedly through many cycles/attempts to maintain ignition.This has...

Bryant Furnace Burner Malfunction [ 1 Answers ]

Hi, We have a 19 year old Bryant gas furnace with a hot surface pilot igniter. The problem is that the pilot lights when the thermostat calls for heat, and then lights the burners which shut down after 15 to20 seconds. It then relights and continues this cycle ten or twelve times before the will...

Bryant Furnace Burner Going On and Off [ 1 Answers ]

Bryant Gas Furnace P/N 394DAC03100 about 30 yrs old. Pilot light stays light and burner going on and off after checking valve problem seems to be some type limit switch when I move the wiring by shaking a little it ignites. Having a problem finding which wires are loosely connected..? If anyone...

Bryant Burner [ 3 Answers ]

I have a valve on a Bryant Burner for an old gas furnace. There seems to be a problem with the gas valve that feeds the burner. Are 40 year old valves available? Thank you. Dennis