    Honeywell RLV310 with Radiant Heat
    Hi, complete newbie here.

    I am replacing the ancient thermostats in my home with the honeywell ones made for radiant ceiling heat. 2 of the 3 I am replacing work fine. The 3rd is wired the same as the others but the heat always stays on. The thermostat shows the temperature reading, but it doesn't cut off when it is supposed to.

    The directions I followed that came with the thermostat are below.

    I have 2 red wires that are the ceiling heat, I have one black and one white wire coming from the circuit breaker, the thermostat has two black wires.

    I connected one of the thermostat wires to one of the red wires, and one of the thermostat wires to the black wire from the breaker, then I connected the white wire to the red wire. I have also tried to switching the reds, and switching the black and white to the red.

    To me, it makes sense that if one of the wires from the breaker is connected to one of the ceiling wires then the heating elements will always have power and therefore always heat... but the directions say to do it this way.

    Can I connect both red wires to one of the thermostats black wires, and both wires from the breaker to the other thermostat wire?

    Please help... it's getting cold here in central PA.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Nov 19, 2009, 02:16 PM

    Your manual is here: http://www.honeywellcentral.com/ssi/...ers-Manual.pdf

    The insructions seem way too simple to mess up. I hink you wired it correctly, but remove the thermostat ans see if the heater turns off. It better.

    It's normal for a solid state switch (TRIAC) to fail shorted,

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Radiant heat questions [ 1 Answers ]

Hi There I plan on installing a boiler etc. to heat the main floor with stapled up underfloor radiant heat and the basement with baseboard type heating. The main floor would have 5 zones. The basement would have 3 baseboard zones. My thoughts for the main floor is to have the kitchen, living...

Radiant Heat addition [ 3 Answers ]

I am trying to add radiant floor heat to a old room that had electric baseboard heater. I currently heat the rest of my house with a pump driven boiler with radiant heat. I would like to tap into this existing system. But because of the allowable space in the new room. I am only going to be...

Radiant floor heat [ 5 Answers ]

Anyone have any experience with repairing busted pex tubing under a slab? I have a customer that would like to fix it without busting up the entire back porch,it's brand new,stamped and very expensive. Any help would be great,I just need to locate it to cut out a small square.

Radiant Heat Won't Shut Off [ 2 Answers ]

I purchased an older home about 3 years ago with radiant heat in the ceilings. Recently, one of the bedrooms had the temperature spike al the way up to over 90 degrees. I can't seem to get the temperature to come down. The heat is controlled by a Mears single pole thermostat, model M401. The...


View more questions Search