    Replaced pressure switch and gauge but still not working
    We have a 30/50 pressure switch we replaced along with the gauge it seems to be working OK but then it stops it will click on after reaching 30 and click off at 50 and then all of a sudden it drops to about 12-15 we had a plumber come out and he said to turn off pump and let water build for few hours it does work but I can't keep turning pump on and off all the time ANY SUGGESTIONS?
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Oct 6, 2009, 05:08 PM

    Call back the plumber and let them know that their advice worked. Im guessing that he had a theory, and the theory was,, you well is running dry.. so when you shut pump off, you are letting well refill. If this is indeed the case, there is no easy fix for it, you will have to either lower the pump( or inlet of jet pump), but this can only be done if you have to depth to do it. I say have your plumber back out to gauge the well, or call in a well specialist to find the problem... Please do let us know what they find. Meanwhile, I will think this over and see what I'm missing,, oh, have you checked the pressure switch feed pipe? Lee.
    smw6896's Avatar
    smw6896 Posts: 2, Reputation: 1
    New Member
     
    #3

    Oct 6, 2009, 05:42 PM

    My plumber doesn't seem to think the well is going dry he seemed kind of baffled he checked the pump itself which he replaced about 6 years ago and he says it seems fine we did clean out the pressure feed pipe
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    Oct 7, 2009, 06:30 AM
    my plumber doesn't seem to think the well is going dry
    That's a contradiction! He's already checked for a lowered water table and came up positive.
    And now he's denying his own findings? Did he give a reason he didn't think the water table was being drawn down? Inquiring minds want to know. Regards, Tom
    jlisenbe's Avatar
    jlisenbe Posts: 5,020, Reputation: 157
    Uber Member
     
    #5

    Oct 7, 2009, 09:50 AM

    Is your pump in the well or above ground?

    I'm not clear as to why the well running low on water would cause your pressure to drop to 15# "all of a sudden". Usually that would cause the pressure to drop slowly as water is used, then when the pump cuts back on, it cannot pump back up to 50# since it does not have the water to pump.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #6

    Oct 7, 2009, 04:28 PM
    AM,
    Wouldn't the pump lower the level and when it couldn't pump any more just stop?
    I just can't see the pressure going down slowly. When you run out of water you run out of water fast. One minute you got suction and the next you're sucking air. Just my take on it. Regards, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Intertherm furnace pressure switch not working [ 3 Answers ]

Hi I have a intertherm furnace it is 2 years oid.The light on the panel is blinking twice.Wich says pressure switch open.HOw do I solve thise problem and get my furnace to work again.THANK YOU

Dual fuel rheem furnace not working, defrost control board replaced still not working [ 1 Answers ]

Hello there, I have a Rheem furnace and is only one year old. Recently my furnace didn't come on so I had someone come out and look at it and it turns out it was the defrost board on the heat pump that was bad. I replaced the board with a new one and turned the system on and it worked on heat and...

Pressure Transducer not working? I read 80 psi with Gauge - Replace or not? [ 1 Answers ]

OK, So I'm in the process of adding a sprinkler system to the back yard - and I checked the pressure at the hose bibs w/ a pressure gauge - 80 psi. Well, where the water enters the house (in the basement) there is a pressure reducer "set at 50 psi." I'm under the impression that the thing is...

Replaced air pressure switch [ 1 Answers ]

My Goodman Gas Furnace diagnostic light indicates a faulty air pressure switch or restricted air supply vent. Vent appears clear, vent motor assembly works. I replaced the air pressure switch but the diagnostic light still indicates the same problem. Is there a reset switch or means of resetting...


View more questions Search