    Replacing range wire
    I have a duplex that has a problem with the wire feeding the range on the second floor. It is extremely old and fraying and needs to be replaced. The wire runs through my garage, out the side of the house and along the back of the house (about 12 feet from the ground) into the 2nd floor kitchen.

    Can I replace this wire with UF-B 8/3? (the breaker the range is on is a 40amp double pole). I'd rather not run conduit along the entire length, I'd like to know if I can get away with the UF-B

    Thanks!
    buzzelec's Avatar
    buzzelec Posts: 5, Reputation: 1
    New Member
     
    #2

    Aug 24, 2009, 02:51 PM
    No you need to put in conduit sorry Jim
    bauer09's Avatar
    bauer09 Posts: 94, Reputation: 4
    Junior Member
     
    #3

    Aug 24, 2009, 04:31 PM

    Why?

    What is the purpose of UF-B then? Just so it can be used underground without conduit?

    Is there any other wire I can run outside without conduit? If I do have to use conduit, wouldn't I just run single THWN wires through it then?
    bauer09's Avatar
    bauer09 Posts: 94, Reputation: 4
    Junior Member
     
    #4

    Aug 24, 2009, 04:36 PM
    Not trying to challenge, just questioning -- section 300.5D1 of the NEC 2005 states that UF cable must be protected where emerging from the earth from 18in below grade to 8ft above. Wouldn't that mean if my cable is running on the house higher than 8ft above the ground that I could run it without conduit?
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #5

    Aug 24, 2009, 05:01 PM
    Bauer... I think you are right. The wire is suitable for damp or wet locations.. proper size, adequate fastening and I think you have an acceptable installation. But local codes may tell you otherwise, if you have a local inspector.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Aug 25, 2009, 04:54 AM

    Just curious, what is the UV protection rating for UF cable?
    bauer09's Avatar
    bauer09 Posts: 94, Reputation: 4
    Junior Member
     
    #7

    Aug 25, 2009, 05:56 AM
    It is rated for sunlight exposure

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electric Range wire size [ 3 Answers ]

Want to install 30 inch electric range. What size wire is needed. 30 feet from panel

Connect my 6-3 wire to a range box [ 1 Answers ]

I want to connect my 6-3 wire to a range box Does the wire go in the lug only or in the lug and the copper slot also

What's size wire for my range? [ 4 Answers ]

I'm wiring a 4 prong plug for my new range. The plug provided says it's a 50 amp size 6/2 & 8/2 SRDT?? What do I get for wire and do I need to pick up a 50 amp breaker?

New 4 wire Dryer/Range Outlet [ 8 Answers ]

I have an older style breaker panel where the neutral & ground wires are connected at the same strip! I plan to upgrade the panel to a 4 wire system with a separate neutral & ground, However since I also need to have the service entrance line upgraded also it won’t be until later this year before I...

Changing the actual range from 3 to 4 wire [ 1 Answers ]

How do I make changes to the actual range to convert it from 3 wire to 4 wire? Everyone talks about replacing the wiring cord with a 4 wire cord, but I have an old range that grounds the common to the frame. It seems to me that I have to disconnect the ground to frame connection and install a...


View more questions Search