    New 4 wire Dryer/Range Outlet
    I have an older style breaker panel where the neutral & ground wires are connected at the same strip! I plan to upgrade the panel to a 4 wire system with a separate neutral & ground, However since I also need to have the service entrance line upgraded also it won’t be until later this year before I can have that done.

    For now I would like to change the Dryer & Range over to the new 4 wire outlets, But I’m not sure if it would create any problems connecting the neutral & ground to the same strip in the main panel!
    cdefraia's Avatar
    cdefraia Posts: 14, Reputation: 1
    New Member
     
    #2

    May 16, 2008, 03:40 AM
    Unless the old panel you have is a sub panel the neutral and grounds are not separated.What you have is probably considered the main panel where the wire from the meter goes right to this panel.You can absolutely change over those 220 lines.Even if you get a new service it will still be a three wire system with the ground and neutrals connected to the same bus bar.I am a licensed electrical contractor in New York.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    May 16, 2008, 03:49 AM
    Exactly what cdefraia said.
    If this is your main panel it is absolutely correct.

    No, there is no problem connecting the ground and neutral to the same bar in the main panel, you have no choice.

    There is much confusion with grounds and neutrals and their purpose and where they connect.
    Just remember, IN the main panel/disconnect the neutral is "bonded" to "ground". After that they must remain isolated.
    Dwall174's Avatar
    Dwall174 Posts: 26, Reputation: 1
    New Member
     
    #4

    May 16, 2008, 10:45 AM
    Quote Originally Posted by cdefraia
    unless the old panel you have is a sub panel the neutral and grounds are not separated.What you have is probably considered the main panel where the wire from the meter goes right to this panel.
    Yea it is the main panel that comes from the meter!
    In fact the SE line coming from the meter to the panel is only 3AWG so for me to upgrade my current 100 amp panel to a 150~200 amp panel I also need to have the service line upgraded.


    Quote Originally Posted by stanfortyman
    There is much confusion with grounds and neutrals and their purpose and where they connect.
    I have to admit I was also part of that confusion!

    The new panel I want to have installed has two terminal strips one on each side of the breakers! I just assumed with two strips, one would be for ground & the other for the neutral!

    Thanks all that’s what I though I just wanted to make sure!
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #5

    May 16, 2008, 11:10 AM
    The two strips are for convience, so the ground an neutrals are near the hot(s) of the respective cable.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    May 16, 2008, 01:58 PM
    Quote Originally Posted by KeepItSimpleStupid
    The two strips are for convience, so the ground an neutrals are near the hot(s) of the respective cable.
    EXACTLY.
    If you look closely, you'll see a solid bar connecting the two terminal bars.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    May 16, 2008, 01:59 PM
    Quote Originally Posted by Dwall174
    Yea it is the main panel that comes from the meter!
    In fact the SE line coming from the meter to the panel is only 3AWG so for me to upgrade my current 100 amp panel to a 150~200 amp panel I also need to have the service line upgraded.
    Not just the service line, the WHOLE service.

    That is why it is called a service upgrade, not just a panel upgrade.
    Dwall174's Avatar
    Dwall174 Posts: 26, Reputation: 1
    New Member
     
    #8

    May 16, 2008, 03:34 PM
    Yea I need to get someone out here & give me a idea of what all I will need! I know it’s going to be $$$$
    Quote Originally Posted by stanfortyman
    Not just the service line, the WHOLE service.
    Does that mean the main overhead lines also? Or just the meter & lines going into the house?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #9

    May 16, 2008, 03:58 PM
    If you have an overhead service it means everything from the splices at the service drop down and in.
    The drop is owned and maintained by the POCO, as is the glass meter itself. The pan the meter sits in is typically the responsibility of the homeowner.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Convert Electric Dryer outlet to regular outlet [ 8 Answers ]

I just bought a gas dryer, leaving a funky 3 pronged outlet unused. The outlet was connected to the fuse box as a single circuit and I would like to let the new gas outlet take advantage of this. Is there any problem replacing the 'funky' electric dryer outlet to a regular three pronged outlet,...

Proper 220V wall outlet for range/oven [ 4 Answers ]

I moved a 200V outlet from one side of the kitchen to another. I bought a new range/oven. When I plug in the range/oven, the rang elements work properly, but the oven will not turn on or the clock runs. Does it look like I rewire the 220V outlet incorrectly? If I get a voltmeter, what reading I...

220 range, 110 outlet [ 4 Answers ]

I have recently acquired a range that has 220 plug - the breaker box shows a double 30 amp - can I assume that that is for a range or can I convert a 110 outlet to a 220 or are there ranges that are 110. Help!

Must you re-wire outlet to outlet? [ 8 Answers ]

Hi there. Great site. I am rewiring my 1950's house with plaster walls, older wiring had no ground. Because it is one story, and extremely tight in the attic on the outer walls, I ran a 12/2 home run for the outlets, to a big (1900?) junction box, then "spidered" out to each individual...

Recessed Range Outlet... [ 1 Answers ]

Hello Group, & TK!:D I was wondering if I can install a Range outlet by just nailing the outlet between 2 nailers and if I truly need a box, and if I do, what size box should I use, because the standard junction, ceiling, and outlet boxes don't seem to fit on the outlet itself. Any help really...


View more questions Search