    Outdoor Kitchen Electrical Subpanel Installation
    I am installing a sub panel for my outdoor kitchen/patio area. I'm thinking of putting in a 60amp sub panel so I can expand to an outdoor living area (just north of the "LOT 35" mark on the survey) if I choose to. Here is the drawing:



    I am going to run conduit along the bottom of the house from the main panel, then bury it to the sub panel. What size conduit and wire will I need?

    Thanks.
    splitz's Avatar
    splitz Posts: 2, Reputation: 1
    New Member
     
    #2

    Aug 17, 2009, 11:07 AM

    Here is the profile of the plan:

    Tev's Avatar
    Tev Posts: 232, Reputation: 20
    Full Member
     
    #3

    Aug 17, 2009, 03:07 PM

    Hots and Neutral should be 6 AWG THWN and Ground can be 10 AWG THWN.

    You could technically use 3/4 PVC conduit but I'd recommend 1 inch for easier pulling.

    I'd put a pull point in that conduit run. It looks to be about 360 degrees of bends and that's the max you can go without a pull point. Again, for ease of installation I'd put one just after the last point of attachment to the house. Possibly use an LB, LR, or LL. They should have these at home depot, just ask the guy at the store to show them to you and choose the one that fits your needs. It will take the place of a 90 degree bend.

    Lastly, if there is any part of the conduit run that is not under the concrete you'll need to take it down to 18 inches below grade.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can substandard electrical wiring installation at home produce electrical arching [ 6 Answers ]

Can substandard electrical wiring installation at home produce electrical arching? Then fire?

Electrical subpanel fed from a subpanel: is this allowed? [ 1 Answers ]

Hello: Can I feed an electrical subpanel (or two) from a subpanel to the main? Thanks for your help!

Do I need an Electrical Subpanel? [ 1 Answers ]

I have a 200 amp panel that is aluminum wiring. I had an air conditioner installed, and although it is on it's own breaker, it blows the main, not it's own breaker. It runs for a short time, but it always pops the main, even if almost nothing else in the house is running. Do I need to replace...

Electrical Subpanel [ 1 Answers ]

I have used all the breaker positions in my existing electrical panel. I want to install a subpanel right next to the present one. Are there any code requirements about spacing?

Electrical Subpanel [ 1 Answers ]

I want to install a electrical subpanel(~50 amp) in my garage, if I do not feed the subpanel with a breaker from the main service of the house,would or could I tie into the main lugs of the main service to feed the subpanel? (Using the proper wire size) Would I have to use a ground rod for the...


View more questions Search