    Wiring a 200 amp breaker disconnect
    There was a question about wiring a disconnect, and the answer indicated direction of current through the breaker. What would happen if the disconnect was wired in reverse with the load coming off the top instead of the bottom of the breaker?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jul 1, 2009, 06:03 AM

    I will guess that the line wire is not long enough to reach the Top Side Line of a breaker disconnect.

    A breaker or disconnect switch will work just fine feeding it either way.

    However, Line is traditionally at the top.

    If the Line is connected to the bottom, one the breaker must be rated for back feed, and special labeling must be clearly visible indicating that the Line side is at the bottom.

    This is rarely done, expect in certain situations due to arrange meant of equipment and cabling.

    This will not be allowed if the reason is only due to short cable.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #3

    Jul 1, 2009, 10:58 AM

    It's a clear violation if you ignore the equipment's labeling--where it indicates the line side. (Pretty much what TK said in his fourth line)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Main disconnect breaker kAIC ratings? [ 4 Answers ]

Can I use a 10 kAIC main breaker in a main disconnect or does it have to be a 35 kAIC main breaker? I have a 10 kAIC, 225 amp breaker on hand, and I did not want to have to buy a new 225 amp 35 kAIC breaker if I did not have to. My indoor load center has a 10kAIC, but the outdoor, main disconnect,...

200 amp safety disconnect vs. 200 amp breaker [ 1 Answers ]

I am in the planning stages of installing an automatic transfer switch for my house-Asco 225 amp". While doing this I was going to upgrade my 100 amp service to a 200 amp service. I was also thinking during this upgrade I would like to have some sort of disconnect between the meter and my automatic...

Wiring a combination meter and main disconnect. [ 1 Answers ]

I bought a Square D CQRA200 Meter/main disconnect combination and I expected to see the neutral isolated from the ground. Does the neutral and ground start from the same block?

How to disconnect wiring [ 2 Answers ]

I have a phone jack in my dining room and one in my kitchen. Each jack works properly. My problem is there is also an old wire coming out from beneath the jack cover and is nailed across my kitchen countertop to the other jack and under its cover. I need to remove the wire in order to have a new...

200 amp breaker/disconnect [ 2 Answers ]

I'm needing wiring help. I am wiring a mobile home and at the service pole I'm not wanting to hang the 200 amp breaker box since it's over one foot long and would like to hang a much small box w/ only a lone breaker or disconnect before going to the 200amp breaker panel mounted else where. ...


View more questions Search