    Securing 6-3 w/g NM / knockouts on electrical boxes
    OK, a few questions: (I did not want to start separate threads. Maybe I should have?)


    Q1: What is/are the proper method(s) for securing larger NM such as 6-3 with ground? Do they make staples for this?


    (OK, so that was 2 questions.. )


    Q2: I am using Carlon Super Blue boxes (residential.) The single gang boxes do not have the "tab" that secures the wire. Instead it has a little square held on by 2 spots. Am I supposed to turn this and push the wire in, or am I to knock this out? Also, if I knock out the wrong one, what is a legal way to cover that hole to satisfy NEC 110.12(A)?


    Thanks in advance.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 18, 2009, 01:44 PM
    My answers are in red:

    Quote Originally Posted by GShelton View Post
    OK, a few questions: (I did not want to start separate threads. Maybe I should have?)


    Q1: What is/are the proper method(s) for securing larger NM such as 6-3 with ground?

    Support NM cable 12 inches from each box or fitting, and then no more than every 4.5 ft.

    Do they make staples for this?

    Yes, see:
    Briscon Electric Manufacturing Corp. makers of electrical supplies


    (OK, so that was 2 questions..)


    Q2: I am using Carlon Super Blue boxes (residential.) The single gang boxes do not have the "tab" that secures the wire. Instead it has a little square held on by 2 spots. Am I supposed to turn this and push the wire in, or am I to knock this out? Also, if I knock out the wrong one, what is a legal way to cover that hole to satisfy NEC 110.12(A)?

    Find you box here and install per instructions:
    Carlon Electrical Products

    I think you have this one:
    http://www.carlon.com/Installation_T...nstall-Low.pdf

    Yes, twist out the knockout. I do not think they make a knockout blank for these, so be careful, try not to have to many unused openings. No inspector ever had an issue with a unused KO with these, that I know of.
    Probably because the openings are so small. Try to avoid any as there is no approved method of closing them.



    Thanks in advance.
    GShelton's Avatar
    GShelton Posts: 13, Reputation: 1
    -
     
    #3

    Jun 18, 2009, 01:59 PM

    Thank you!

    The PDF from Carlon (horrible install guide if you ask me. LOL!) shows the box details in the second row, 3rd from the left. It says knockout, so I will go with you on that. (Good thing because I did knock them out. LOL!)

    As for the staples, I do see on that site they have a 1-3/8" long 13/16" wide that is rated for the 6-3. The ones I have are not long enough and just pull out. Off to the supply house for me.

    Thanks again!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

No electrical boxes in the ceiling [ 10 Answers ]

I have been slowly trying to go through my house and change out old brass fixtures in my 19 year old house to more updated fixtures and keep coming across the same problem: simply a black and a white wire poking out a one inch diameter hole in the ceiling with no blue electrical box (or as I call...

NEC 2002 and Electrical Boxes [ 1 Answers ]

I want to replace four fluorescent lights that are under my patio with fans. I removed the lights and it seems that the box is in a 1x3 (the light weighs only a couple of ounces). I am wondering if the code (which Nevada dwellings must comply with) specifies how an electrical box must be mounted...

Electrical boxes [ 9 Answers ]

I was just told by someone that you have to have insulated outlet boxes for exterial walls inside the basement? Is this true? I've never heard or seen these, I've seen them for exterior outlets outside, but not inside.

Electrical boxes [ 1 Answers ]

How can I jump my electrical boxes? I just recently bought an apartment building and I would like to make it one whole house and I would like to run the downstairs apartment to upper.. there are to separate boxes that run each apartment side by side.. I was told I could "jump" one box from the...

Electrical boxes [ 2 Answers ]

I think I have an unique problem. I have a 4"x4"x6' space which is all wall board above a pass through. I have 3 small wall sconces I want to mount above the pass through. The problem is the wall board. How do I attach the electrical boxes so I can mount the light fixtures? At this point I have the...


View more questions Search