    KingsX Posts: 231, Reputation: 10
    Full Member
     
    #1

    Feb 20, 2009, 04:45 PM
    How concerned should I be with my Knob and Tube?
    My house has knob and tube, with only two circuits. One circuit runs all the lights on the main floor (bungalow). The second one is for all the outlets on the main floor, plus all the lights in the basement (maybe 5 fixtures), plus one only outlet in the basement.

    When I moved in, there was two thirty amp fuses in those two circuits, which is obviously wrong and dangerous. I switched them back to 15 amp fuses each. Now I have to be careful not to run the microwave and the coffee machine at the same time, but shockingly, its working out.

    My house was built in 1921 and I couldn't tell you when those thirty amp fuses went in, or if they have been swapped through time, or what. So my concern is, being that this wire is old, could the constant extra heat over that time have degraded the wire so bad, that even now that I have 15 amp fuses in there, I have a serious fire risk? I have a 16 month old daughter and another on the way, and I all of a sudden got very paranoid. I plan on replacing the electrical, but its going to take some time. What do you guys think?
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #2

    Feb 20, 2009, 04:59 PM

    If the K&T wiring was severely overloaded, it could be degraded. However, correctly done K&T is pretty safe if you don't continue to overload it. Don't change any devices or move any wires if you can help it. Flexing could cause insulation to fall off and then you have to go to shrink tubing and all that to save it. Possibly your house is wired with #12 wire which would be rated at 20 amps, which would be better than #14, but don't go upping the fuse rating without being CERTAIN it ALL is #12 on a circuit. Don't lose any sleep, but get it changed when you can afford it. I've lived with it almost all my life.
    KingsX's Avatar
    KingsX Posts: 231, Reputation: 10
    Full Member
     
    #3

    Feb 20, 2009, 05:02 PM

    We've managed with 15 amp circuits, so I don't see a point anyway in changing it. We do have a sub panel with updated wiring for the stove, fridge, some more outlets in the basement, and garage etc. So thankfully I don't have to worry about those. But, still all bedroom outlets, living room etc are on that original k&t. I did replace the outlet in my daughters room with a gfci. And I've had to replace the odd light switch, but didn't see any crumbling or damage inside the box.
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #4

    Feb 20, 2009, 05:34 PM

    If you didn't see any problems in device boxes, I doubt that there's too much damage elsewhere. Most junctions on the actual wires are soldered, so they are pretty immune from heating if done correctly. And since your heavy draw appliances are on modern wiring, you should be safe with the correct fuses.

    Sleep well.

    EPM

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Knob and tube, no ground. [ 7 Answers ]

I have knob and tube. All of my outlets on the main floor are in the floor as opposed to the wall. I have direct access to the boxes from the basement. The outlets aren't grounded (except for some, you'll see later). Pretty much all of the outlets are really old, and fairly worn out. This makes me...

Knob & Tube [ 1 Answers ]

I am currently remodeling my bathroom. Home built in the 50's with existing knob and tube. Bathroom has power coming into 1 switch that controls lighted medicine cabinet with outlet inside cabinet. Want to add 1 new light fixture, 1 GFI, and 1 ceiling fan (no light). Is there any diagram that...

Replacing Knob and Tube [ 3 Answers ]

I'm looking for a little clarification here. I'm in the process of replacing the Knob and Tube wiring in an older 1930 home. Although I trying to preserve the original look of the house the K&T prevents me from installing insulation in the attic. Originally there was only one circuit running into...

Tieing in to knob and tube [ 3 Answers ]

When tieing in 14/2 at switch box, what do you do with the neutrals?

Knob and Tube tie-in [ 13 Answers ]

I apologize if I missed this info elsewhere. I have an 80 YO bungelow with seemingly healthy knob and tube wiring. The house has a combination of old and new wiring depending on when past work was done. My question is what is the safest, code friendly or preferred way to mate the old K&T to new...


View more questions Search