    Replacing Knob and Tube
    I'm looking for a little clarification here. I'm in the process of replacing the Knob and Tube wiring in an older 1930 home. Although I trying to preserve the original look of the house the K&T prevents me from installing insulation in the attic.
    Originally there was only one circuit running into the attic that serviced all the lights in the house. I would like to run two circuits up there instead of one and split the load. That way if I happen to trip a breaker I’m not left completely in the dark.

    From my service panel my electrical lines run through conduit into my basement and from there it runs up to the attic. I know I can run two lines of 12-2 Romex from my panel up to the attic to service the lights but I’m also trying to conserve space through the conduit.
    So here is my question: Can I run a single 12-3 line up to my attic to service all my lights? If I run the black wire on one circuit and the red wire on another circuit (out of phase with the first circuit) can I share the common wire? From what I’ve read, and please correct me if I’m wrong, the common will carry the difference between the loads. I’m using a 20A breaker which should allow me a 1900W load safely. I’ve estimated a maximum of 1400W per circuit if all the lights were on and I used 100W bulbs.
    Also, if I’m correct and I can run my line in this manner, is there any reason why I shouldn’t.

    Any help would be appreciated,

    Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 29, 2007, 02:36 AM
    Yes, you can use a 3 wire cable for two circuits that share the neutral. Be sure the two circuits are on each on opposite legs at the panel.
    goofy_guy's Avatar
    goofy_guy Posts: 2, Reputation: 1
    New Member
     
    #3

    Oct 29, 2007, 10:50 AM
    Thanks TK, I was pretty sure it wasn't a problem but it's always better to get a second opinion.
    Thanks again,
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Oct 29, 2007, 12:10 PM
    You can save even more room in the conduit as far as it goes, by running THHN or other singles.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Knob and tube (adding a switch and fixture) [ 6 Answers ]

First let me say hello everyone and second let me tell you all that I am very new to knob-and tube wiring... I hope I can explain this enough to get some help from you all. Ok here goes... I have been trying to figure this out for some time... I wanted to replace a ceiling fixture in my dining...

Tieing in to knob and tube [ 3 Answers ]

When tieing in 14/2 at switch box, what do you do with the neutrals?

Tieing knob and tube to 14/2 [ 1 Answers ]

Can someone please tell me how to tie knob and tube wiring into 14/2 wiring. This is a hundred plus year old house and I want to upgrade... Thank you Lou G.

Replacing dip tube [ 2 Answers ]

Hi everybody. I just moved into a new house, it has a 90 (!) gallon gas-fired hot water tank. Despite this, my showers start to run cold pretty quickly. I opened the tank's drain faucet -- no rust or lime coloring in the water at all. Same with the pressure relief valve. So, I am thinking it...

Knob and Tube tie-in [ 13 Answers ]

I apologize if I missed this info elsewhere. I have an 80 YO bungelow with seemingly healthy knob and tube wiring. The house has a combination of old and new wiring depending on when past work was done. My question is what is the safest, code friendly or preferred way to mate the old K&T to new...


View more questions Search