    Kyburz's Avatar
    Kyburz Posts: 2, Reputation: 1
    New Member
     
    #1

    Jan 7, 2009, 12:22 AM
    Baseboard Heater Removal
    I recently eliminated a base board heater in my bedroom which is the furthest from the electrical. The 220 wire comes from the top of the stud wall down to where the heater use to be.

    My question: Are these heaters typically hooked up (connected) in tandom? Can I go back to the baseboard in the previous room and disconnect the wire coming out of the baseboard? I want to discharge the line and leave it in the wall.

    Thanks for any help on this.

    Kyburz
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jan 7, 2009, 05:41 AM
    Depends on where the thermostat is. If it is on the unit, AND there is only one cable in the heater, then the line could come from another heater on that circuit or right from the panel.
    If there is a wall stat then it likely comes right from there, if there are no other heaters on that thermostat.
    Kyburz's Avatar
    Kyburz Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 7, 2009, 10:29 PM

    The heater was on an outside wall. The themostat is on the inside wall perpendicular to the outside wall. So, you are saying that the electrical source for the heater runs to the thermostat and then to the heater. So, it is likely on its own circuit?

    New Question: What the best way to discharge the electrical source. At the thermostat? Or at the panel? Or where?

    Thanks for the input!

    Kyburz
    21boat's Avatar
    21boat Posts: 2,441, Reputation: 212
    Ultra Member
     
    #4

    Jan 7, 2009, 11:35 PM

    Always use the circuit breaker to "discharge" anything and put a piece of tape on the flipped breaker so know one accidentally turns it back on while working on the branch circuit.
    If you do discharge the line and want to leave it in the wall it has to be totally disconnected from its source or at the panel box. If panel box pull wire off breaker and cut wire no mistakes on re energizing it. Mark breaker left in box and tag disconnected.
    I would get a cheap tester at least and check what's hot and what's not.

    Signed 21 Boat

    If I Helped To Answer Your Question Please
    Rate My Answer

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Baseboard heater [ 1 Answers ]

We bought a marley 2545 baseboard iwe connecting adopuble pole thermostat to it on the left endheater has 2 black wires the theromstat has a red and black wire and groung heater says you can wire to either end but the right end has a black and red wire how do I do this we are only wiring on...

Baseboard heater [ 1 Answers ]

I recently changed all the heaters and thermostats in my house with brand new heaters and programmable thermostats. All heaters are wired to 15 amps double pole breakers with the appropriate size wire(14 is it? It was inspected so it is the right size). In my living room, I changed the 2000 heater...

Baseboard Heater [ 2 Answers ]

Hello, I tried wiring a 240v baseboard heater using a double-pole breaker and single pole thermostat. I connected both white and black at the breaker, paid attention to line/load using the black at the thermostat, wire nutted the white, and connected at the heater per instructions. When I...

Baseboard Heater Help! [ 2 Answers ]

Hi there. I have recently wired my entire house with brand new Dimplex baseboard heaters and thermostats. All of the heaters work great but the problem is the thermostats are not working correctly. The heaters turn on as soon as you move the stat dial past the lowest setting. They will...

Baseboard Heater [ 1 Answers ]

I'm wiring a 240v 1500w heater and I ran a #12 wire because the circuit is also going to double as a A/C circuit for the summer. Anyhow I followed the wiring diagram on heater and wired to a 2pole 15amp and I turned on breaker and it popped so I pulled apart the heater and looked it all over again...


View more questions Search