    I recently changed all the heaters and thermostats in my house with brand new heaters and programmable thermostats. All heaters are wired to 15 amps double pole breakers with the appropriate size wire(14 is it? It was inspected so it is the right size). In my living room, I changed the 2000 heater for a 2500 watts. There is also a 750 watts on the circuit. Correct me if Im wrong, but the load on a breaker should not be higher than 80% of the total load the breaker can take. So 80% of (15amps x 240 volts) gives me 2880 watts. So technically I am good, but I somehow worry if I should have kept the original size for the heater. All is fine, no breakers are popping and both heaters work good. Am I just worrying for nothing?

    Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 26, 2007, 02:54 AM
    The 80% rule is a safety factor for the circuit breaker, no overcurrent protection device shall exceed 80% of it's rating, unless the OCPD is rated to be loaded at 100%, which most are not, and certainly your is not..

    Then, a branch circuit conductor shall be rated 125% of the load. So 2500 w + 750 w=3250 watts x 125%=4062.5 watts /240volts = 16.93. The wire must be #10 wire on a 30 amp circuit breaker. You are really pushing the 15 amp circuit with #14 wire.

    Electric heat is considered as a continuous load, and these safety factors are universal for any load, and are very typical.

    Sorry but I see no other choice but to reduce load on the circuit. You can check with your inspector to double check me, but he should see it the same way.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I Paint a Baseboard Heater? [ 2 Answers ]

I have searched in different forums here, and no thread seen. We are doing some remodelling in our guest room, and I need to know if I can paint the top and face of a 240v baseboard heater? Thanks for any advice.

Baseboard Heater [ 2 Answers ]

Hello, I tried wiring a 240v baseboard heater using a double-pole breaker and single pole thermostat. I connected both white and black at the breaker, paid attention to line/load using the black at the thermostat, wire nutted the white, and connected at the heater per instructions. When I...

Baseboard Heater Help! [ 2 Answers ]

Hi there. I have recently wired my entire house with brand new Dimplex baseboard heaters and thermostats. All of the heaters work great but the problem is the thermostats are not working correctly. The heaters turn on as soon as you move the stat dial past the lowest setting. They will...

Baseboard Heater [ 1 Answers ]

I'm wiring a 240v 1500w heater and I ran a #12 wire because the circuit is also going to double as a A/C circuit for the summer. Anyhow I followed the wiring diagram on heater and wired to a 2pole 15amp and I turned on breaker and it popped so I pulled apart the heater and looked it all over again...

Baseboard heater help [ 2 Answers ]

I have to replace a missing baseboard heater 110 volt 1500 watt all I can find at home depot Lowe's etc is 220 volt can I use one of those hooked to 110 I do understand the output would be lower but actually don't need that much heat in that room anyway Thanks Gene


View more questions Search